I'm runing a 60 amp sup panel to a shed under ground and need to know what size rnc to use
AJPOLCARI is offline   Reply With Quote
Old 10-01-2012, 10:05 AM   #2
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
MC is not listed for direct burial. Use UF or PVC conduit. I recommend the PVC.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 10-01-2012, 10:05 AM   #3
Electrician
Assuming THWN, they are legal in 3/4", but depending on the length of the run & number of bends, you might want to consider stepping up To 1".
dawizman is offline   Reply With Quote
Old 10-01-2012, 10:08 AM   #4
Electrician
He said rnc, so I assumed he was referring to pvc, but it's probably good to clarify.
Old 10-01-2012, 11:06 AM   #5
JOATMON
ddawg16's Avatar
Rewards Points: 812
AJ....ever hear the phrase "You learn by your mistakes"?
While 'technically', the THWN will fit in a 3/4" conduit.....don't do it....
I would go 1" min....cost difference is minimal....you will spend a lot less time cussing as you try to pull those wires.
I have 1"...same size wire....and I bet the same sub panel.
In fact....1 1/4" conduit would be even better....
And....make sure you use THWN, not THHN. THHN is not rated for wet conditions...though, most of the THHN you get now days is marked THHN/THWN.
Oh...and the ground can be bare copper.
Old 10-01-2012, 02:37 PM   #6
Ntwrk. Systems Engineer
I recently ran your exact config, except I used #8 THHN wire for the ground. Although 1" ended up being fine with a couple 90 degree elbows to get around a deck, I ended up doing a test fit, running the bundle, and assembling as I went over the 75' span because it was tight. You could probably preassemble and use a machine to pull it, but I didn't.
5th_Time is offline   Reply With Quote
Old 10-01-2012, 05:46 PM   #7
Master Electrician
Rewards Points: 3,678
r n c is printing out to look like mc.
brric is offline   Reply With Quote
Old 10-02-2012, 08:57 AM   #8
1" would be easiest. I pulled 4 #6 wires about 90' in 1" with several 45's and a few 90's. Pull boxes make a big difference and make the job easier.
I ran 3 #6 wires in 3/4" about 30' with a couple pull boxes. It was definitely a tighter fit, I wouldn't want to do it with 4 wires and a longer distance.
OKDrew63 is offline   Reply With Quote
50 Amps for a garage help IcyShadowz Electrical 48 05-31-2012 11:58 PM
Size AWG cable and conduit for long runs wwurzba Electrical 2 03-30-2012 11:44 AM
Ground wire size for 200A subpanel? jaserlet Electrical 0 11-10-2011 09:50 PM
Connecting new dishwasher and garbage disposal -- no ground wire in the conduits. arca Electrical 17 03-28-2011 03:06 AM
220 Ground wire size. Giles Electrical 2 01-30-2010 09:22 PM