Hi, I am installing a new meter base, 100 amp panel, and re-locating the laundry room.
I ran 100 amp 4 gauge? wire from the meter (underground) to the panel. I used 2" conduit where it comes out of the trench and into the house, and into the panel.
My question is, can I put other wires in the conduit with the 4 gauge? It would end up with the 3 conductors for the panel and a 12 gauge 2 conductor wire, and a 10 gauge 3 conductor wire.
This will get inspected and I want to get it right the first time.
Thanks in advance!
gogetter is offline   Reply With Quote
Old 02-06-2013, 12:19 AM   #2
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
Is this a just a meter you are starting at or is it a combo meter load center?
Sent from my iPhone using DIY Forum
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 02-06-2013, 12:23 AM   #3
rrolleston's Avatar
Also the 4 gauge wire is that AL or CU?
Old 02-06-2013, 12:30 AM   #4
Sorry, Not a meter/LC combo. Meter is about 40' away from the panel. Wires are aluminum.
Old 02-06-2013, 12:34 AM   #5
rrolleston's Avatar
#4 wire is only good for 65 amps and this is unfused conductors you can't run anything else in there from your meter.
The Following User Says Thank You to rrolleston For This Useful Post:
NJMarine (02-06-2013)
Old 02-06-2013, 10:34 AM   #6
Okay. The wire us #2 aluminum. It is fused at the meter with a 100 amp breaker.
Old 02-06-2013, 11:00 AM   #7
Rewards Points: 236
Table 310.15(B)(7) allows for #4 CU wire for a 100 amp service or #2 AL.
OP. Never try to pull cables into conduit. The 2" PVC conduit is plenty big enough. But you are never going to pull anything else over the wires you already pulled unless you are willing to sacrifice one of them..
Why would you need more wires in the service lateral anyway? You cannot feed the structure with more than one service/supply.
Why not be a bit more specific as to why you would want to add any wires to this service conduit.
Old 02-06-2013, 11:14 AM   #8
I was hoping to come back out of the panel with 2 circuits to feed my laundry (from the outside). I was hoping to put them back out the conduit that the #2 wires are in to save piping in more conduit.
The #2 wires are in a 2" conduit, which I believe is bigger than necessary.
Sorry for the confusion, it makes sense looking at it, but hard to explain.
Old 02-06-2013, 02:25 PM   #9
rrolleston's Avatar
Once you pass the first disconnect you must go to a four wire feed with grounding at the disconnect and your building.
Since this is past his first disconnect I don't think 310.15(B)(7) would apply here. And a four wire feed would be required.
Old 02-06-2013, 02:55 PM   #10
Thanks for your help. I quit being lazy and run another conduit for the additional wires. I'll also add a #6 copper ground wire back to meter, where the ground rods are.
Conduit fill Sunny B. Electrical 10 10-25-2011 08:22 AM
Buried gas pipe in conduit WillK Plumbing 4 01-07-2011 12:50 PM
NEC- National Electric code 2008 Scuba_Dave Electrical 7 04-19-2010 04:41 PM
Need help with conduit fill calculations kornbln Electrical 6 07-28-2009 12:22 PM
Would you spring to fill in your backyard? Piedmont Landscaping & Lawn Care 4 05-14-2009 08:14 PM