Conduit De-rating - Electrical - DIY Chatroom Home Improvement Forum
Old 07-28-2009, 04:44 PM   #1
Conduit De-rating
How much derating will occur if I run 3 2awg and 1 4awg in a 1.5" EMT conduit? Breaker is likely to be a 75Amp. 2 conductors will be hot legs.
angrysmileyface is offline   Reply With Quote
Old 07-28-2009, 04:50 PM   #2
Why would you think there would be derating?
According to conduit fill calc I see 1.25" being OK
1.5" conduit should be fine
Old 07-28-2009, 04:56 PM   #3
Just checking, Im in the mode where I like research all parts of a problem
Old 07-28-2009, 07:49 PM   #4
Rewards Points: 2,350
You only derate for current carrying conductors, not conduit size. If this circuit is fed from a single phase 120/240 V source, then you only have two current carrying conductors, so no derating is required. Over three conductors is when you begin to derate.