I am thinking of using raceway to add an outlet to an existing circuit. Can I run THHN wires through the raceway or must I use Romex? And what would be the maximum fill for 1/2" raceway? Would 3 12 AWG THHN wires, or 12/3 Romex, fit safely?
brookny is offline   Reply With Quote
Old 11-11-2011, 10:11 AM   #2
Rewards Points: 130
THHN for raceway (conduit). Romex requires no raceway and is considered a cable. 3, #12 wires in a 1/2" conduit is just fine. You could add more if needed. THHN must be in a raceway/conduit.
The Following User Says Thank You to J. V. For This Useful Post:
brookny (11-11-2011)
Old 11-11-2011, 10:23 AM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,192
The raceway must be in a dry location to use THHN. For conduit in wet locations use THWN or dual rated THHN/THWN
Coastal South Carolina
Old 11-11-2011, 12:25 PM   #4
It is indoors, but terminating within 2' of a kitchen sink, at a GFCI receptacle. That's still considered dry, right?
Old 11-11-2011, 12:32 PM   #5
A "Handy Husband"
rjniles's Avatar
That is dry.
The Following User Says Thank You to rjniles For This Useful Post:
Old 11-11-2011, 10:45 PM   #6
Missouri Bound's Avatar
What is it that you are calling a raceway? Are you referring to a surface mount moulding?
Old 11-12-2011, 05:30 AM   #7
Electrical Contractor
kbsparky's Avatar
Wiremold is a UL listed raceway....
-KB
Old 11-12-2011, 12:02 PM   #8
I'm using wiremold
Old 11-12-2011, 12:38 PM   #9
I'm using wiremold
The wiremold should have fill capacity listed somewhere in the packaging or paperwork.
Tags
conductors , raceway
Confusion over how many conductors in an electrical box dharper Electrical 11 07-08-2011 07:43 AM
Sizing Motor Branch Circuit Conductors and OCPD's electures Electrical 5 06-22-2011 11:32 PM
Making holes in junction boxes WillK Electrical 18 05-26-2011 06:21 PM
Marking buried cable a7ecorsair Electrical 15 07-20-2010 12:27 AM
non current carrying conductors davidbp Electrical 14 05-09-2010 10:09 PM