-   -   Conductors in Raceway (http://www.diychatroom.com/f18/conductors-raceway-123086/)
brookny 11-11-2011 09:15 AM
I am thinking of using raceway to add an outlet to an existing circuit. Can I run THHN wires through the raceway or must I use Romex? And what would be the maximum fill for 1/2" raceway? Would 3 12 AWG THHN wires, or 12/3 Romex, fit safely?
J. V. 11-11-2011 10:11 AM
THHN for raceway (conduit). Romex requires no raceway and is considered a cable. 3, #12 wires in a 1/2" conduit is just fine. You could add more if needed. THHN must be in a raceway/conduit.
rjniles 11-11-2011 10:23 AM
The raceway must be in a dry location to use THHN. For conduit in wet locations use THWN or dual rated THHN/THWN
brookny 11-11-2011 12:25 PM
It is indoors, but terminating within 2' of a kitchen sink, at a GFCI receptacle. That's still considered dry, right?
rjniles 11-11-2011 12:32 PM
That is dry.
Missouri Bound 11-11-2011 10:45 PM
What is it that you are calling a raceway? Are you referring to a surface mount moulding?
kbsparky 11-12-2011 05:30 AM
Wiremold is a UL listed raceway....
brookny 11-12-2011 12:02 PM
I'm using wiremold
Missouri Bound 11-12-2011 12:38 PM
Originally Posted by brookny (Post 769456)
I'm using wiremold
The wiremold should have fill capacity listed somewhere in the packaging or paperwork.