Compressor Question - Electrical - DIY Chatroom Home Improvement Forum
Old 02-20-2010, 06:38 PM   #1
Compressor Question
I have an Ingersoll Rand 80 gal 5 HP compressor that is 220 or 230. When an electrician hooked it up for me in my shop he used 10 gauge. Is it necessary to use 10 gauge or would I be fine with 12 gauge? I have searched all over the net for the manual to my compressor and can't find it.
Electrical Wonderer is offline   Reply With Quote
Old 02-20-2010, 07:14 PM   #2
Rewards Points: 1,016
There should be a placard on the compressor that states power requirements - what does it say? Did the electrician see the unit? He likely sized the circuit off the unit.
It probably draws around 20a or more running - more at start-up, so would go on a 30a breaker with #10 wire - #12 would be a 20a breaker and not enough circuit.
Old 02-20-2010, 08:19 PM   #3
joed's Avatar
Rewards Points: 11,516
Compressor is motor circuit. It works on different rules than standard circuits. Even if it is 30 amp it might be able to be installed on #12. I'm not that up on motor circuits but I do know you are allowed smaller wires for them than normal circuits if you wish.
Old 02-20-2010, 10:50 PM   #4
Suggest to contact Ingersoll Rand for their recommendations if you can't find a manual and definitive answer.
Old 02-20-2010, 10:54 PM   #5
Just call me Andrew
Rewards Points: 1,020
Why can motor circuits have smaller wire?
Andrew
secutanudu is offline   Reply With Quote
Old 02-20-2010, 10:55 PM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Not likely that a 5 hp motor will be able to use #12 awg. If you have no motor manual then the compressor would be wired to the motor rules of the NEC. A 5 hp motor has an FLC of 28 amps at 230 volts. The minimum ampacity for the wires in the branch circuit would be 1.25 x 28 = 35 amps. The minimum wire you could get by with is #10 awg.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 02-21-2010, 01:00 AM   #7
Exclamation
No. Not smaller than the FLA (Full load amperage) of the motor! You're allowed to oversize the protection by 25% (125% of FLA) due to starting draw, which falls back to normal rating after initial starting surge!!
spark plug is offline   Reply With Quote
Old 02-21-2010, 01:12 AM   #8
Rewards Points: 410
I have a dedicated 20 amp to my 2hp compressor.
I had a 15 amp at my old place that trip the breaker in cold
weather starts.
High Gear is offline   Reply With Quote
Old 02-21-2010, 07:14 AM   #9
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
Actually, if you use a breaker to protect the circuit you can go up to 250% of the motor FLA. 300% for non-time delay fuses and 175% time delay fuses.
If that comes out to a value of a non standard fuse/breaker rating, you can go to the next higher standard value.
wirenut1110 is offline   Reply With Quote