Ropegun 01-20-2011 08:37 PM
Compressor Motor
Hi to everyone here.
I have an electrical rookie problem in hopes that I'll get my solution from some of you guys.
I'm trying to hook up a motor for a compressor and want to know if it's possible to do so at 120V. The info for the motor:
Magnetek Century AC Mtr
Cat#323
Volts 230-208/115
RPM 1725
HP 3/4
This is a decent sized compressor with a 30 gal tank. It was hooked up in an industrial warehouse but I was curious if can be hooked up at 120V.
The schematic on the motor terminal box shows a hook-up for a high and low voltage hook-up. Is the low good for 120V? It would be ideal to be able to wire an SO cord into it and plug it in to a regular receptacle.
If I connect the terminals (accordingly) I should be able to turn it into a 120V hook up right? Making one of the leads a neut and the other the hot?
Any help at all is much appreciated.
joed 01-20-2011 08:42 PM
The 230-208/115 would indicate that it can be wired for 120 volts.
110 115 120 all the same voltage.
J. V. 01-21-2011 12:18 PM
Cat#323
Volts 230-208/115
RPM 1725
HP 3/4
120 volts is fine for this motor. But it will draw significant current (amps). The NEC allows up to a 30 amp breaker for this motor. You can try a 20 amp circuit and see first.
This 3/4 Hp motor at 120 volts draws 13 amps. But the motor will draw many times this amount of current at start up.
The NEC calculation for this motor is 13 x 2.50 = 32.5 amps. This indicates you may need a 30 amp circuit to accommodate the starting current.
Try plugging it into a 20 amp circuit first and see if it starts, runs and cycles.
Ropegun 01-21-2011 08:20 PM
Thanks for the reply. Any hints on how to hook-up the terminals. There are 6 and if I remember correctly #2 and #3 are not used. Terminal #1 has a yell w/blk stripes, #4 is red, #5 is brn & org, and #6 has blk and yell. Terminals #1 & #2 are line's. Would you or anyone else out there happen to know the correct configuration for a 120V hook-up? This is the 'low' voltage hook-up according to the schematic that has both a 'low' & a 'high' voltage hook-up, but I'm just confused if the 'low' they mean isn't the 208 and not the 120. I'm assuming the 'high' voltage hook-up is for 230.
-Thanks again.
jbfan 01-21-2011 10:14 PM
Low voltage hook up is 120 volt.
High voltage would be 208/240 volt.
Ropegun 01-21-2011 10:21 PM
Much appreciated! :thumbsup: -so then (without beating a dead horse to...well, death) I guess it doesn't matter which lead I make a neutral as long as it is followed through all the way to panel that way...right?
J. V. 01-22-2011 10:51 AM
Thats right. Don't forget the ground wire. H-N-G. I would use a dedicated circuit. :thumbsup:
Ropegun 01-23-2011 01:25 PM
Thanks a bunch for the help.:thumbup: