Code Change For Equipotential Bonding?? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-09-2013, 03:42 PM   #1
Rewards Points: 506
Code Change for Equipotential Bonding??
From a dated post: Does this mean that not all Spas, Hot Tubs, Pools need the Equipontential Bonding?
Tentative Interim Amendment
NFPA 70
National Electrical Code
2011 Edition
Reference:
680.42(B)
TIA 11-1
(SC 11-3-10/TIA Log #1005)
Pursuant to Section 5 of the NFPA Regulations Governing Committee Projects, the National Fire Protection Association has issued the following Tentative Interim Amendment to NFPA 70®, National Electrical Code®, 2011 edition. The TIA was processed by Panel 17 and the National Electrical Code Technical Correlating Committee, and was issued by the Standards Council on March 1, 2011, with an effective date of March 21, 2011.
A Tentative Interim Amendment is tentative because it has not been processed through the entire standards-making procedures. It isinterim because it is effective only between editions of the standard. A TIA automatically becomes a proposal of the proponent for thenext edition of the standard; as such, it then is subject to all of the procedures of the standards-making process.
1. Revise 680.42(B) to read as follows:
680.42(B) Bonding.
Bonding by metal-to-metal mounting on a common frame or base shall be permitted.
Exception No. 1: The metal bands or hoops used to secure wooden staves shall not be required to be bonded as required in 680.26.
Exception No. 2: A listed self-contained spa or hot tub that meets all of the following conditions shall not be required to haveequipotential bonding of perimeter surfaces installed as required in 680.26(B)(2):
(1) Is installed in accordance with manufacturer’s instructions on or above grade
(2) The vertical measurement from all permanent perimeter surfaces within 30 horizontal inches (76 cm) of the spa to the toprim of the spa is greater than 28 inches (71 cm).
Informational Note: For further information regarding the grounding and bonding requirements for self-contained spas and hottubs, see ANSI/UL 1563 – 2009,Standard for Electric Spas, Equipment Assemblies, and Associated Equipment.
Issue Date:
March 1, 2011
Effective Date:
March 21, 2011
(Note: For further information on NFPA Codes and Standards, please see
www.nfpa.org/codelist)
Copyright © 2011 All Rights Reserved
NATIONAL FIRE PROTECTION ASSOCIATION
Installation is the Reverse of Removal.
Old 05-09-2013, 05:06 PM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Only spas and hot tubs, it ends up costing more than the tub itself in most cases, and really serves no purpose. Your state must accept this TIA before you can just stop doing what is required by the NEC.
http://www.nfpa.org/Assets/files/Abo...1005NFPA70.pdf
Old 05-09-2013, 10:58 PM   #3
Rewards Points: 506
Right, Stickboy, I meant Hot Tub.
Reading the TIA that you linked to, I guess they've determined that, in some cases, the EB could do more harm than good!
For an in-ground spa, the perimeter grid adds to the safety by unifying the shell and the surrounding deck to one potential because all are in electrical contact with the earth.
In contrast, the self-contained spa shell is non-conductive, and the internal structure, while bonded together, is electrically isolated from the earth requiring grounding back to earth-neutral. In the event of a ground fault, the presence of a neutral-earth bonded perimeter grid in the deck will lower its impedance, increase fault current, and guarantee a current return path through the victim!
A storable pool, already excluded from the equipotential grid requirement of the NEC, would present the identical aggravated shock hazard if a bonded perimeter grid were installed.
Old 05-10-2013, 08:18 AM   #4
Rewards Points: 720
My understanding is that the TIA was instituted as an exception for existing surfaces at the request/screaming of the Hot Tub manufacturers. Basically that EPZ bonding rule made it illegal to install a hot tub on an existing deck or patio due to the lack of the grid.
Mark
busman is offline   Reply With Quote
Old 05-10-2013, 03:58 PM   #5
Rewards Points: 506
Mark
hmm, I don't know, Mark. According to the .pdf that Stickboy linked, my understanding was that EQP Bonding made self contained spas more dangerous due to lessened impedance.
How would this work?
I didn't read the entire report, but I didn't see that which you refer to.
Old 05-10-2013, 05:06 PM   #6
Rewards Points: 720
I'll stand by my post. The submitter was "
Carvin DiGiovanni, Assn. of Pool and Spa Professionals
They did not argue that the EPZ makes it less safe. They argued that since it is astronomically expensive to install the grid for existing surfaces that people were at risk by installing Spas with no inspections, because inspectors were implementing crazy expensive things to meet the code EPZ requirements.
Mark
Old 05-10-2013, 05:22 PM   #7
Rewards Points: 506
Mark
I'm not trying to be argumentative, but how, then, do you interpret the following: "the presence of a neutral-earth bonded perimeter grid in the deck will lower its impedance, increase fault current, and guarantee a current return path through the victim!"
Old 05-10-2013, 05:45 PM   #8
Oso954's Avatar
Rewards Points: 442
I didn't read the entire report, ....
That is part of the problem.
If you go back to it, there is a diagram that will help. It is labeled "
Shock Hazard in a Self-Contained Spa with Bonded Perimeter Grid"
Notice that on the left, the say "faulty or no GFI". They also assume a ground fault. Then you couple those with the lessened impedance.
So, under those conditions, it would be more dangerous. But it isn't something to lose sleep over.
Oso954 is offline   Reply With Quote
Old 05-10-2013, 05:55 PM   #9
Rewards Points: 506
Originally Posted by Oso954 View Post
"faulty or no GFI".
Yes, along with "... with Bonded Perimeter Grid", so that, to me, is saying that a grid makes it more dangerous in the event of a fault.
Of course, this is with a "self-contained" spa
Old 05-10-2013, 06:35 PM   #10
Oso954's Avatar
Rewards Points: 442
If you are worried about the increased danger of a self contained spa with a bonding zone, then don't buy the spa. Have an in-ground one built instead.
Old 05-10-2013, 06:43 PM   #11
E2 Electrician
Its also a ridiculous requirement when installing one on a deck... it just makes no sense, and the fact that they ARE portable, from a cost aspect, to remove and install another EBG is just plain right insane to request.
Old 05-10-2013, 07:49 PM   #12
Rewards Points: 506
I ain't worried about it, I'm just trying to get the lowdown
The issuance of the TIA, and accompanying investigative reports, simply peaked my desire to understand EB.
Please note that I do not understand this requirement, so hence, my thread.
It seems that most regard it as an attempt to save cost, and indeed, I did read about the consequences of the requirement as it pertained to unpermitted, and rogue work.
So, is it a general consensus that EB doesn't need to be installed in self-contained, portable, or above ground spas/hot tubs?
Old 05-10-2013, 07:51 PM   #13
Rewards Points: 506
What about on a deck that has perimeter metal, say within 5', or with metal handrails, or whatever?
Old 05-10-2013, 07:52 PM   #14
E2 Electrician
Only if your state accepts the TIA in its amendments.
Old 05-10-2013, 07:59 PM   #15
Rewards Points: 506
I've heard this said before
The Following User Says Thank You to sirsparksalot For This Useful Post:
stickboy1375 (05-10-2013)
error code 45 Turtle learner HVAC 2 01-10-2011 05:09 PM
code details for boxes kama Electrical 6 01-30-2009 11:25 AM
Which bonding method proper??? Nestor Electrical 2 09-15-2006 07:18 AM
International building code and permits rforsha Building & Construction 4 08-28-2006 07:35 PM
1950's Roof Framing Strength KempLN Building & Construction 21 06-17-2006 11:06 AM