Clothes Dryer Tripping Main Breaker - Electrical - DIY Chatroom Home Improvement Forum
Old 08-26-2011, 05:39 PM   #1
Clothes dryer tripping main breaker
I have a clothes dryer that runs sometimes and other times bypasses the 30a breaker it is on and trips out the main. The dryer comes from a breaker in a feed through outdoor panel. Everything seems tight on both ends, it doesn't seem to pull more than expected with an amp meter on it. Not sure what else to do? The only other thing that looks weird is: the line coming in from the meter goes to the lugs on bottom of panel, then feeds through breakers, then main is bolted on, then it feeds the house. Does this seem right?
bkc1974 is offline   Reply With Quote
Old 08-26-2011, 06:37 PM   #2
Electrical Contractor
kbsparky's Avatar
I sounds like you have a reverse-fed feed-thru panel.
As long as there are less than 6 total breakers out there, it should qualify as proper service equipment.
You have said that it trips the main, yet the dryer continues to operate once that main is tripped? Is that correct? Does it ever trip its own breaker?
Does that main breaker feel warm to the touch when it trips out?
-KB
Old 08-26-2011, 10:18 PM   #3
I=E/R
a7ecorsair's Avatar
You didn't tell us what size main you have. To help you understand what may be happening, let's assume you have a 100 amp main breaker. With the dryer off, let us also assume your panel load from everything in the house is 80 amps. You now turn on the dryer and add another 25 amp load to the panel. The dryer breaker won't trip but now the main has 105 amps against it...
There is also a possibility that one side of the panel has a much higher load than the other side.
a7ecorsair is offline   Reply With Quote
Pool Main breaker keeps tripping beckyreyes Electrical 12 08-11-2013 04:06 PM
Main Breaker goes off.... spiral Electrical 6 01-01-2011 07:18 PM
Garage Fridge Tripping Breaker in Cold Weather aaronjwood Electrical 10 12-24-2010 06:47 PM
Intermittent circuit, breaker not tripping lucabrasi Electrical 5 03-14-2010 07:03 PM
New electric dryer is blowing breaker! minameismud Electrical 7 09-14-2008 10:45 PM