Circuits In Garage And GFCI - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-24-2012, 03:00 PM   #16
Originally Posted by Jim Port View Post
That exception has also been removed.
For clarification, my locality (Cabarrus County, NC) has not yet adopted the 2011 NEC code and is still going by the 2008 code. As such, I have to install an equipotential bonding grid around my portable hot tub which would not be the case with the 2011 code.
Best Regards,
Ted
tedallen is offline   Reply With Quote
Old 05-24-2012, 03:08 PM   #17
Is there a specific code requirement regarding how close a receptacle in the garage may be to a service entrance door? Also, any minimum/maximum height from floor requirement if installed on a wall as opposed to in the ceiling?
There is an existing GFCI receptacle that I need to relocate to make room for the second breaker panel I am installing and one option is to install it in the narrow stud cavity between the new panel and a service entrance door. Also, if going that route, would there be a code issue with mounting the outlet within a studs width of the main breaker panel (the breaker panel door and the outlet cover might come close to touching one another). If I attempt to use the existing wiring running to/from the GFCI receptacl I would most certainly have to raise the receptacle higher on the wall in the new location.
Also, is there a code prohibiting installation of receptacles for two different circuits in a common gang box (e.g. a 2-gang box with a receptacle as part of a 20 amp circuit and a receptacle as part of a 15 amp circuit, GFCI or standard)?
Best Regards,
Ted
Old 05-24-2012, 06:35 PM   #18
Licensed electrician
Rewards Points: 1,612
No issue with either having 2 circuits in a common box or with a receptacle close to the panel or a service door.
The two grounds from the circuits need to be connected together.
tedallen (05-24-2012)
Old 05-24-2012, 06:55 PM   #19
Jim,
Do you mean that the two ground from the different circuits need to be connected together within the gang box (the line side of each circuit tied together and also connected to the ground screws of the load devices in the gang box) or do you mean that the grounds need to be connected back at the source of the circuit run on a common ground bus (or neutral bus if bonded to the ground bus)?
When using a dual-lug meter box with two main breaker panels (each having neutral and ground bonded together), would you want to connect the grounds from circuits originating from the two different panels together or only circuits originating from the same breaker panel? Since both panels have neutral bonded to ground and both are being supplied a common neutral from a single meter box, the grounds are already tied together at the origination point regarldess of which panel the circuit originates from. Is this correct?
Best Regards,
Ted
Old 05-24-2012, 07:03 PM   #20
I was assuming you wanted something like two receptacles, each on one circuit in a 2 gang box. In this case the bare or greens are tied together to each other and to the devices.
Garage GFCI keeps tripping faromic Electrical 7 08-30-2011 10:45 PM
Garage Door GFCI jamiedolan Electrical 7 07-31-2011 09:14 PM
Garage GFCI Circuit Wiring Problem woodworkerjeff Electrical 23 04-06-2011 12:34 PM
Garage GFCI Circuits H2O Engr Electrical 6 01-20-2010 07:22 PM
GFCI in detached garage question WShawn Electrical 2 08-02-2008 03:27 PM