Circuit Breakers For Solar And/or Generator? - Electrical - DIY Chatroom Home Improvement Forum
Old 02-04-2014, 10:26 AM   #1
Rewards Points: 173
Circuit Breakers for Solar and/or Generator?
Hello,
I am making some changes to my home electrical panel with remodeling and trying to plan for the future. Eventually I will add a grid tie-in solar electrical system, as well as whole-house generator (with automatic transfer switch). Will I need to make room on my main panel for circuit breakers to address these or will the electrical connection typically be handled in another way?
There are various options for this, but it seems as though I have seen a wiring diagram that showed the main utility electrical feed going from the meter into equipment that coordinated it with the solar electrical and generator feed, THEN to the main electrical panel for the house downstream. Regardless, circuit breakers on the panel were not addressed.
Peace,
Dr. Z.
Zeigh is offline   Reply With Quote
Old 02-04-2014, 11:00 AM   #2
47_47's Avatar
Rewards Points: 58
I've got a whole house generator with an ATS. Incoming (generator and street) power is routed into the ATS, then to the main panel. Nothing in my main panel was changed.
I do not know how a solar system would tie into this.
47_47 is offline   Reply With Quote
Old 02-04-2014, 12:35 PM   #3
JW
mm11's Avatar
Rewards Points: 614
When using a interactive PV system, the breaker from the inverter must be landed opposite the service.
The breaker must be suitable for backfeed- not marked 'Line' and 'Load'.
The ampacity of the breaker cannot exceed 120% of the rating of the bus in the panel- if the bus is rated at 200 amps, the maximum size of the breaker from the inverter cannot be more than 40 amps.
mm11 is offline   Reply With Quote
Old 02-04-2014, 07:38 PM   #4
JW
mm11's Avatar
Rewards Points: 614
Revision- the breaker cannot exceed an additional 20% of the ampacity of the bus in the panel.
Circuit Finder and Tandem breakers?? Skelleyman Electrical 7 10-22-2012 02:06 PM
Main circuit breaker's screws hot even with breaker off? darlingm Electrical 13 01-15-2012 11:44 AM
Outlets on 2 circuit breakers? travesty Electrical 8 04-05-2011 09:19 PM
2 breakers / 1 circuit dn100 Electrical 3 10-03-2010 08:01 PM
Sub-Panel or Tandem Circuit Breakers? dgoldsmith Electrical 2 03-08-2008 12:34 PM