Hello, in my house I have 2 breakers that are outputting 220v. Each breaker is 20 amps and I am wondering if the total current can be 40 amps or if it is only 20?
Then what gauge wire will I need to support this power?
Thank you!
pclever1 is offline   Reply With Quote
Old 01-31-2014, 09:14 PM   #2
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
Thank you!
20a 240v.
12g wire would work with it.'
"facts" have no relevance to this discusion
Posting from a concrete bunker under a non descript barn
plummen is offline   Reply With Quote
The Following 2 Users Say Thank You to plummen For This Useful Post:
micromind (01-31-2014), pclever1 (01-31-2014)
Old 01-31-2014, 09:15 PM   #3
Electrical Enthusiast
Rewards Points: 504
If you have one double pole 20 amp breaker, you have 240 volts 20 amps. Theoretically, you could have 20 amps on either leg and have 40 amps worth of 120 volt loads, but that is not how it is described.
12 awg is what is usually used with 20 amps circuits. What is this circuit feeding? (Or going to feed?)
Kyle_in_rure is offline   Reply With Quote
Old 01-31-2014, 09:18 PM   #4
They both tie into one cable leading to a humidifier that draws 17amps.
What is the point of the second breaker then, is it just to double the voltage?
Old 01-31-2014, 09:44 PM   #5
Rewards Points: 504
They both tie into one cable leading to a humidifier that draws 17amps. What is the point of the second breaker then, is it just to double the voltage?
Each breaker serves a 120 volt leg. Your transformer puts out two 120 volt lines (I believe 180 degrees out of phase), put the two legs together and you have 240 volts. The motor uses both legs and therefore uses 240 volts.
It's similar to having a 120 volt hot wire and a neutral, except instead of a neutral you have another 120 volt line.
The arrangement is called "split phase" power.
The Following 2 Users Say Thank You to Kyle_in_rure For This Useful Post:
Tags
220v , amperage , breaker , current
Dead circuit, couldn't find problem so tied into second circuit zappy12 Electrical 25 12-13-2012 10:38 PM
main circuit breaker amperage kupalino Electrical 13 12-23-2009 09:32 PM
900W and up trips breaker, Circuit draws power even with everything off... jasonblu Electrical 40 12-09-2009 03:29 PM
Heat pump circuit breaker pbms pinkertonpv HVAC 11 02-18-2009 10:47 AM
Adding new circuit breakers to 100 amp sub panel DrP Electrical 8 05-25-2006 11:05 PM