Circuit Breaker, Working In Reverse - Electrical - DIY Chatroom Home Improvement Forum
Old 04-06-2009, 01:02 PM   #1
Circuit Breaker, working in reverse
I have found a nice and small load center to replace my inside fuse box. The box, which is carried at Lowes, uses a 220 circuit breaker as the box main breaker. This means the breaker would need to work backwards, IE the constantly powered end is the breaker wire attachment point.
Does this work? is this allowable? Would it pass an inspection?
This breaker in not a built-in breaker. It is a normal 220 V 100A breaker, installed in one corner. I should have dug around in the box further, when I was there, for an explaination.
dcwestcott is offline   Reply With Quote
Old 04-06-2009, 01:13 PM   #2
Remodeling Contractor
If this was the built-in breaker, yes it will work fine. This is how a main breaker needs to work.
Old 04-06-2009, 01:25 PM   #3
Yes this is perfectly normal - if replacing your main 60 amp Edison base fuse box use nothing smaller than a 100 amp circuit breaker load center. Your question also worries me too - You do know that most poco's won't re-energize your house without a licensed electrician signing off on it right?
hychesee is offline   Reply With Quote
Old 04-06-2009, 02:23 PM   #4
Yes, Unfortuneatly, I do.
Old 04-06-2009, 03:03 PM   #5
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
What your describing is a panel that utilizes a 'backfed' double pole breaker as a main with an installed hold down. The breaker is probably 100 amps. Assuming this panel will be used as your main panel (service equipment) fed from the meter base you need to verify if you have a 100 amp service entrance otherwise you may have too large of a main breaker for the proper protection of the service entrance wiring.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Main Circuit Breaker Test lthomps222 Electrical 16 11-07-2010 04:40 PM
Just for fun Andy in ATL Electrical 56 10-20-2009 09:33 AM
What is the meaning of KA(kilo amps) of a miniature circuit breaker? wkyong Electrical 2 09-12-2008 12:39 AM
Do I need to replace my circuit breaker box? greenlantern Electrical 7 08-11-2008 11:27 PM
HELP!!! Info on changing old fuse box to circuit breaker box BryanR Electrical 2 03-12-2006 04:26 PM