Circuit Breaker That Trips Slowly - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 09-07-2010, 06:25 PM   #16
Rewards Points: 876
Originally Posted by Shyster & Shyst View Post
The quick way of determining if the breaker is at fault (before buying a new one) is to temporarily move the wire from the breaker that is slow-to-trip to the breaker next to it. If you get the same results as with the first breaker then the problem is between the breaker and the fan.
I had a similar problem recently with lights in the upstairs bath. Everythign pointed to a bad breaker. Turns out that the neutral wire (white) was loose at the breaker box.
Just want to caution you here:
Before doing what you describe, make sure that the breaker next to the suspect one has the same rating!
You don't want to be putting a 15A circuit onto a 20A breaker!
FW
Ultrarunner2017 is offline   Reply With Quote
Tags
bathroom fan , circuit breaker
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Heat pump circuit breaker pbms pinkertonpv HVAC 11 02-18-2009 09:47 AM
New GFCI Breaker trips with no load bmurphywa Electrical 6 04-06-2008 08:48 PM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM
So lost - electrical requirements please help lapsis9 HVAC 4 12-20-2006 08:09 PM