-   -   Circuit breaker question (http://www.diychatroom.com/f18/circuit-breaker-question-59551/)
kupalino 12-18-2009 10:05 PM
I'm adding a circuit breaker for receptacles in my basement and I'm wondering if using Square D Ground Fault 20-AMP circuit breaker (I think this has built in GFCI) with regular receptacles is the same as using a regular circuit breaker with GFCI receptacles down the line.
thanks.
Scuba_Dave 12-18-2009 10:06 PM
Yes you can use a GFCI breaker instead of a GFCI outlet
These are different from AFCI -arc fault
So make sure you get the right one
Yoyizit 12-18-2009 10:14 PM
Troubleshooting ground fault problems will be easier with indiv. GFCIs.
Scuba_Dave 12-18-2009 10:26 PM
That's true
So it depends upon what you are going to be plugging in & what you will be wiring
But...my pool cabana has had a GFCI breaker for all outlets & lights for 10+ years without a problem
I have since added more circuits....
micromind 12-18-2009 11:22 PM
GFI receptacles are far less costly than breakers.
If you use the receptacles, and one trips, it's much easier to reset than going out to the panel.
Rob
vsheetz 12-19-2009 12:00 AM
Rob
X2 on both counts.
kbsparky 12-19-2009 12:35 AM
Rob
Depends on where the receptacle vs the panel are located. :yes:
In the case of outside receptacles, venturing between snow covered bushes trying to reset an errant GFCI device is much more inconvenient than a trip to the utility room and opening the breaker box door. :whistling2: