Old 02-17-2017, 09:23 AM   #1
Rewards Points: 6
Circuit breaker question
I'm installing a 100 amp sub panel to feed some additional circuits. This panel will only feed 120v circuits. My question is, can I use one side of a double pole 100 amp circuit breaker to feed the sub panel from the main panel?
Kroshsis is offline   Reply With Quote
Old 02-17-2017, 09:34 AM   #2
Licensed electrician
Rewards Points: 1,754
Re: Circuit breaker question
Even with only 120 loads you can still use both legs to feed the panel. You can probably use a smaller feed if you run 2 hots.
Old 02-17-2017, 09:36 AM   #3
Rewards Points: 6
Thanks for the reply Jim, but can I do as I mentioned and run off of just one side of the breaker?
Old 02-17-2017, 09:39 AM   #4
Rewards Points: 406
Only one half of the slots will work... Which begs the question, are you also planning to place a jumper wire from one leg to the other or double up wires somehow? (So both legs will work.)
So far as I know, that would not be allowed. And in my opinion you should do it right or not at all.
brric likes this.
Justin_99 is offline   Reply With Quote
Old 02-17-2017, 09:57 AM   #5
Master Electrician
Rewards Points: 3,918
Why would you even consider this ? The cost of one additional conductor can not be that prohibitive.
Please explain your reasoning.
Speedy Petey likes this.
brric is online now   Reply With Quote
The Following 3 Users Say Thank You to brric For This Useful Post:
Jim Port (02-17-2017), mpoulton (02-17-2017), Speedy Petey (02-17-2017)
Old 02-17-2017, 10:10 AM   #6
The cost might be able to be offset by running smaller conductors and conduit. The plan certainly is not the best way to add a panel. Perhaps the OP thinks if 120/240 is run they need 240 loads.
Old 02-17-2017, 10:43 AM   #7
Rewards Points: 6
My primary reason for this question is to not have to use that much larger conduit for the extra 1ga line. Not sure I can get all the conductors in 1 inch conduit and not have a heating problem.
Old 02-17-2017, 10:59 AM   #8
Oso954's Avatar
Rewards Points: 1,300
Using both legs of a 50 amp breaker carries the same power as using one leg of a 100 amp breaker.
You wouldn't be on "1 ga".
Oso954 is online now   Reply With Quote
The Following User Says Thank You to Oso954 For This Useful Post:
Old 02-17-2017, 12:07 PM   #9
Semi-Pro Electro-Geek
Rewards Points: 2,970
A 50A 4-wire feeder fits fine in 1" conduit. I would not try to run a 100A 3-wire feeder in 1" conduit though. There is absolutely no reason to use a 120V-only feeder for this panel.
Speedy Petey, Jim Port and Oso954 like this.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is online now   Reply With Quote
Circuit Breaker Question Rik R. Electrical 3 02-23-2014 04:38 PM
Circuit breaker testing newbie question kyryk Electrical 22 08-05-2012 09:12 AM
Did My GFCI Circuit Breaker Fail? Jazan Electrical 8 08-04-2012 03:44 PM
Circuit Breaker Question Bob Deb Electrical 15 11-29-2010 07:34 PM
Circuit BReaker Question - breaker didn't trip and no power thru the circuit Ronin_67 Electrical 2 08-08-2008 06:06 AM