Circuit Breaker Doesn't Trip - Electrical - DIY Chatroom Home Improvement Forum
Old 02-09-2011, 10:10 PM   #1
circuit breaker doesn't trip
Light circuit quit working 12 years after house was built (homeowner built, passed state inspections, no problems). Four 2-pole switches, no outlets, grounded. No light works, breaker does not trip (swapped breaker, no change) 115 VAC, breaker to ground/neutral at breaker panel . 115 VAC across switch terminals, on OR off, all four switches. In sockets, 48 VAC when switch is on, 0.2 VAC when switch is off. Doesn't make sense to me. What should I look for now?
harryevan is offline   Reply With Quote
Old 02-09-2011, 10:15 PM   #2
Rewards Points: 506
When you realize 115v across an OFF switch, is there a bulb in the socket?
jlmran is offline   Reply With Quote
Old 02-09-2011, 10:58 PM   #3
Yes, but it isn't lit.
Old 02-09-2011, 11:05 PM   #4
Rewards Points: 506
Where are you placing the probes when measuring at the socket?
Old 02-09-2011, 11:14 PM   #5
" Euro " electrician
frenchelectrican's Avatar
Sound like you have open netural so read the the voltage at the switch by useing one of the hot conductor and ground { bare } you should get 120 volts if so then you have open netural.
To find it you have to check the affected junction box like other switch box or at the recpectale near the switch box.
{ there are some case you may have a hidden juction box which I know some homeowner or other dolt do that and hid the junction box or worst is flying splices both items are illegal per any electrical codes.}
Merci.
Marc
Old 02-09-2011, 11:50 PM   #6
Rewards Points: 506
Wouldn't an open neutral reveal itself at the switch? He has 115v across an open switch.
Unless all 4 light sockets have loose neutral connections at each of their respective pigtails. Unlikely.
Again to OP: where are you placing the probes?
Old 02-09-2011, 11:58 PM   #7
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
sounds like open neutral to me also,strange
plummen is offline   Reply With Quote
Old 02-10-2011, 12:04 AM   #8
Maybe so but if he have 4 single pole switches the quickest way is he have to find the netural connection in the switch box which it will show up majtory of the time unless the OP have 4 switch loops then it will be pain in arse to sort it out so if he did have netural at the switch box I will check both netural and ground to the hot to make sure the reading is correct.
If the OP understand what we are try to do this test and it should not be very hard at the switch box at all.
That is basic 101 either you have it or you don't !
Merci.
Marc
Old 02-10-2011, 12:13 AM   #9
Rewards Points: 506
If voltage is the same across the switch terminals in either position (on or off), then it strangely sounds like 4 bad switches. They're not closing.
Old 02-10-2011, 12:20 AM   #10
It will be nice if he posted the photo then we can able indentify it very quick.
For me that should only take couple minutes to verify it { by reading H-G to rule out the open netural that is the only place it may have poor connection on netural.}
To OP did you use the DVM if so they are pretty sentive with ghost voltage so get a test lamp that useally rule it out.
Merci.
Marc
Old 02-10-2011, 12:38 AM   #11
plummen's Avatar
Merci.
Marc
youve got 4 single pole switches on 1 fixture? they must have differant wiring in canada,it would be rather strange in nebraska!
Old 02-10-2011, 12:54 AM   #12
I do not know where the OP is from however with 4 gang switch box 99% of the time I work on them they will always have line et netural there it don't matter if that is in North Americian side or European side the rules still the same.
So that is quick way to tell and I betcha that useally a bad netural connection that is the cuprit. { I get pretty good percentage with bad connection as I mention above like backstabbed receptales or bad wirenut splices that those two are most likely cuprit }
Merci.
Marc
Old 02-10-2011, 01:00 AM   #13
plummen's Avatar
no im saying 4 single pole switces connected to same fixture is a little strange,2 3ways and 2 4s on one fixture i can understand
Old 02-10-2011, 01:09 AM   #14
Ahh ok I am getting your point on that the only time I ever see that if you have very large chandler luminaire then it will make sense otherwise .,,
But I will address to the OP the two pole switch is not often used sound like 4 way or three way set up. { the three way switch will have three screw connections while two pole and four way will have 4 screws but both are not interchangeable they function diffrent}
Merci.
Marc
Old 02-10-2011, 01:11 AM   #15
plummen's Avatar
Tags
Federal Pacific stab-lock circuit breaker Mike in Arkansas Electrical 4 11-29-2009 09:07 PM
Insulation around a electrical circuit breaker box terpsing Electrical 4 02-03-2009 03:08 PM
Circuit BReaker Question - breaker didn't trip and no power thru the circuit Ronin_67 Electrical 2 08-08-2008 06:06 AM
How Does A Double Pole Circuit Breaker Trip? shadowx360 Electrical 2 07-09-2008 02:44 PM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM