Chronic Lightbulb Failures In Can Lights - Electrical - DIY Chatroom Home Improvement Forum
Old 04-20-2009, 12:14 PM   #1
Chronic lightbulb failures in can lights
I have a set of 6 can lights on a two-switch setup in my kitchen.
I had a problem with the incandescent bulbs burning out in 2 of the fixtures in a couple of days. It was always the same 2 fixtures. Using "long life" halogena bulbs they lasted for a week or two.
I switched to CFL floods and they last for 1-2 months.
I'm calling a friend who is an electrician, but do you all have any ideas?
What should I troubleshoot for?
TexasEd is offline   Reply With Quote
Old 04-20-2009, 01:38 PM   #2
BIGRED
Rewards Points: 252
It sounds like a heat problem combined with a can fixture that is too closely insulated and can not gain sufficient cooling. Do you have bulbs at or below the rated wattage for the fixture?? Can you get at the fixtures from up above?? If not go online to LEDLIGHT.com and look up household LED bulbs. They have 3 and 5 watt bulbs that are every bit as comparable as 60 watt halogen or 40 watt CFL bulbs and they do not get warm.
Grampa Bud is offline   Reply With Quote
Old 04-20-2009, 01:55 PM   #3
The CFL that popped last night did so after it had been off for 5 hours. It audibly popped when I turned the switch on.
Also these lights are in the space between the first floor and the second floor. I do not expect there to be insulation there but I will check.
Old 04-20-2009, 02:57 PM   #4
Higher than normal voltage [126v to 132v], but it can't be as high as 240v or they wouldn't last that long.
Vibration due to people stomping around or due to resonance with machine vibrations?
Abnormal temp. in just those two fixtures?
Loose connections/bad wirenuts in just those two fixtures?
Old 04-20-2009, 07:19 PM   #5
Resident Electrician
Here are a few things I would look at.
First thing I thought of was too much insulation around it. If the can lights can't breathe, they will NOT work correctly. Bud was correct. I have saw contractors put insulation between two floors a thousand times. Yours should have it there.
Second take the can apart from the inside and get to the make up inside the junction box. Get a meter and check your voltage from Hot to Ground, and Hot to Neutral. You should be anywhere from 115v to 125v.
Third it sounds like maybe could be a loose neutral. Take all the wire nuts off the wires and replace with new Ideal tanny wire nuts. http://www.foxelectricsupply.com/con...uctNo=IDE30341
Also check your socket where the bulb screws in. Make sure it looks clean and nothing is broken inside it.
Get back to me and let me know if any of those worked.
thefamouscbc is offline   Reply With Quote
Old 04-21-2009, 10:50 AM   #6
Tool Geek
PaliBob's Avatar
Rewards Points: 2,160
Here is a recent similar thread
Recessed light - lamps burning out
Note on the chart that for this can the manufacturer says 40W max for Incandescent bulbs (A19)
Disclaimer
& Stay Safe
.....Bob Lavery
Old 04-21-2009, 11:03 AM   #7
What I don't get is, are the two that burn out the problem, or are the four that don't burn out the real symptom [that is, all six should be burning out and the ones that aren't are especially hardy]?
This problem doesn't seem possible which means I, for one, am assuming something that isn't true.
Old 04-21-2009, 12:15 PM   #8
Tool Geek
PaliBob's Avatar
Are the 2 problem cans IC
Could the installer have put in IC cans at the problem area?
This manufacturer not only severly restricts lamp wattage and envelope but also makes a point:
For use with 120V
Incandescent lamps
Nothing in there about CFL's
source:
http://www.cooperlighting.com/specfi...RICT_RICAT.pdf
Disclaimer
& Stay Safe
.....Bob Lavery
Old 04-21-2009, 01:08 PM   #9
Rewards Points: 1,548
I contend that a CFL will work anywhere an incandescent of the same voltage and wattage will work assuming a direct connection to power (i.e. no electronic gadget such as a dimmer in between).
Old 04-21-2009, 01:12 PM   #10
The other thread has me wondering about the bulb size as well. I am using what the builder installed for the size of the bulbs, but they could have installed the wrong size. I have been using BR30 floods. I'll remove the bulbs to see if I can find a model number on the cans to look up the recommended bulbs.
I will also check to see if all the cans are the same model. (I think it would be bad to assume they were)
Old 04-21-2009, 01:16 PM   #11
Alan,
There are no dimmers on this circuit.
Old 04-21-2009, 04:58 PM   #12
Except for starting temp. restrictions which don't apply here, I have to agree.
The lighter current draw may cause switch contacts to self-clean less effectively, but that is also not a factor here.
Old 04-21-2009, 06:36 PM   #13
Electrical Contractor
kbsparky's Avatar
You have bad sockets. Loose connections on the rivets that hold the screw-shell assembly together can overheat and cause premature failure of bulbs. Even CFL's can literally cook to death.
Replace the socket assembly, and your problem should vanish.
Old 04-21-2009, 09:37 PM   #14
Can loose sockets be confirmed by inspection? Is this a factory defect?
Old 04-21-2009, 10:09 PM   #15
kbsparky's Avatar
Sometimes, you can see scorch marks on bad sockets. Loose fitting screw-shell or bottom tab flattened out and cracked can also be determined by visual inspection.
But not always.
As for factory defects, maybe. But how old are these fixtures anyways? More likely worn out from years of service.
Finding underground electric wire for driveway lights. mitch21131 Electrical 25 09-24-2012 08:52 AM
New lights in basement CooperChloe Electrical 11 01-11-2009 11:22 AM
undercabinet puck lights ccalmonte Electrical 7 08-05-2008 08:25 PM
Adding can lights to an existing circuit TexasEd Electrical 1 06-17-2008 07:23 PM
Pot lights in a drop ceiling Howdy Electrical 3 03-14-2008 08:23 PM
