Christmas Lights - Amps
Christmas Lights Run 250 feet from house to a tree near road. There is an outlet. Extension cord. Split to many extension cords then split to many lights. Also split after first EC to a few extension cords going to two wreathes. The lights are LEDs and it says 90 stands take less than 2 amps. We have had amp issues before but want to know if the distance of extension cord itself takes amps? Or does it just supply the one/two amps?
( Lower volts make amps rise ) But if you use a good size cord (thick as poss') and if the load is low, like only 2 amps then the loss will be very small not enough to worry too much about. |
Just to give you an idea of how minimal the voltage loss is with LEDs.
1000 ft of #16 wire (typical light duty extension cord) has about 2.5 ohms of resistance. So 2 amps of current would result in 2 * 2.5 = 5 volts lost in the resistance of the extension cord, leaving a nominal 120 - 5 = 115 Volts available to the LEDs. |
I think the general concensis is -
Running a load of 2 amps over 250 ft will not be a problem. The only time it becomes a problem is with bigger loads, So if your getting up around 10 amps or so, A thicker power lead would be required. A good rule of thumb is for long runs of cable you should double the current rating, So instead of using a cord rated for 10 amps use a cord rated at 20 amps. And to be technially correct leads dont eat up amps, instead they eat up volts. |
| All times are GMT -4. The time now is 12:27 PM. |