Question
charging subpanel ... more questions
1. do i use the same kind of circuit breaker to charge a subpanel as i would for a regular circuit?
2. if i use a 100A circuit breaker on the main panel to charge the subpanel, will AWG 3 wires suffice for black/red/neutral? and can i go smaller for the ground?
thanks
Old 08-15-2012, 02:09 PM   #2
Electrical Contractor
kbsparky's Avatar
The minimum size of equipment grounding conductor for a 100 Amp feeder or circuit is #8 copper.
The #3 feeders are fine.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
amakarevic (08-15-2012)
Old 08-15-2012, 06:37 PM   #3
can i go smaller than 3 AWG. i am gonna go with a cable, not loose conductors actually
Old 08-15-2012, 06:50 PM   #4
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
What is the amperage rating for the sub-panel ?
Old 08-15-2012, 07:11 PM   #5
Master Electrician
If its being fed off a 100a then it has to be #3
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
The Following User Says Thank You to andrew79 For This Useful Post:
Old 08-15-2012, 08:12 PM   #6
200 but i am feeding it off of a 100A circuit breaker in the main panel. I got a bigger amperage because i may switch it to its own meter in the future
Old 08-15-2012, 08:57 PM   #7
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If you are using AL cable to feed the sub you need 2/2/2/4.
Old 08-15-2012, 10:19 PM   #8
kbsparky's Avatar
That #2 SE cable is only good for 90 Amps max ....
-KB
Old 08-15-2012, 10:23 PM   #9
k_buz's Avatar
looked at the wrong column. As you can tell, we don't use much AL wire here.
Old 08-15-2012, 10:36 PM   #10
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Dont worry, most guys around here use table 310.15(B)(6) when wiring subpanels.
Old 08-15-2012, 11:00 PM   #11
"So I Re-Wired It"
MisterZ's Avatar
Umm, were you referring to 310.15(b)(16)??
Knowledge is Power, but 240v can Keel You!!
MisterZ is offline   Reply With Quote
Old 08-15-2012, 11:03 PM   #12
k_buz's Avatar
No I think he is referring to 310.15(b)(7) in the 2011 code. He is still using the 2005...(b)(6) was changed to (b)(7) in the 2011.
The Following 2 Users Say Thank You to k_buz For This Useful Post:
MisterZ (08-15-2012), stickboy1375 (08-15-2012)
Old 08-15-2012, 11:06 PM   #13
"So I Re-Wired It"
MisterZ's Avatar
Ahh thanks, i have 08 and 2011..... maybe we should ask cossac what he thinks. Hahaha.
Try to out-funny me now Stickboy
The Following User Says Thank You to MisterZ For This Useful Post:
stickboy1375 (08-16-2012)
Tags
subpanel
Subpanel to outdoor workshop RM575 Electrical 22 08-01-2012 10:59 PM
Adding subpanel next to main box insane_drummer Electrical 25 06-10-2011 11:39 AM
Adding a subpanel to a sub-panel and other questions CardinalPilot Electrical 14 03-30-2011 03:23 PM
Subpanel installation in outbuilding fls Electrical 19 03-16-2008 03:19 PM
Reverse Polarity at the Subpanel adm060306 Electrical 14 07-09-2007 01:58 PM