amakarevic 08-15-2012 12:54 PM
1. do i use the same kind of circuit breaker to charge a subpanel as i would for a regular circuit?
2. if i use a 100A circuit breaker on the main panel to charge the subpanel, will AWG 3 wires suffice for black/red/neutral? and can i go smaller for the ground?
thanks
kbsparky 08-15-2012 02:09 PM
The minimum size of equipment grounding conductor for a 100 Amp feeder or circuit is #8 copper.
The #3 feeders are fine.
amakarevic 08-15-2012 06:37 PM
can i go smaller than 3 AWG. i am gonna go with a cable, not loose conductors actually
Stubbie 08-15-2012 06:50 PM
What is the amperage rating for the sub-panel ?
andrew79 08-15-2012 07:11 PM
If its being fed off a 100a then it has to be #3
amakarevic 08-15-2012 08:12 PM
200 but i am feeding it off of a 100A circuit breaker in the main panel. I got a bigger amperage because i may switch it to its own meter in the future
k_buz 08-15-2012 08:57 PM
If you are using AL cable to feed the sub you need 2/2/2/4.
kbsparky 08-15-2012 10:19 PM
That #2 SE cable is only good for 90 Amps max ....
k_buz 08-15-2012 10:23 PM
:censored: looked at the wrong column. As you can tell, we don't use much AL wire here.
stickboy1375 08-15-2012 10:36 PM
Dont worry, most guys around here use table 310.15(B)(6) when wiring subpanels. :no:
MisterZ 08-15-2012 11:00 PM
Umm, were you referring to 310.15(b)(16)??
k_buz 08-15-2012 11:03 PM
No I think he is referring to 310.15(b)(7) in the 2011 code. He is still using the 2005...(b)(6) was changed to (b)(7) in the 2011.
MisterZ 08-15-2012 11:06 PM
Ahh thanks, i have 08 and 2011..... maybe we should ask cossac what he thinks. Hahaha.
Try to out-funny me now Stickboy;)