-   -   Changing 220V to 110V (hardwired) for an electric to gas cooktop switch. (http://www.diychatroom.com/f18/changing-220v-110v-hardwired-electric-gas-cooktop-switch-92074/)
charleyhart 01-12-2011 09:39 AM
I am changing over my kitchen island cooktop from electric to gas. The electric cooktop is hardwired (in a junction box) 220V. If I change out the circuit breaker (from 220V to 110V) in the fuze box, is there any reason why I would need to change the wiring from 10 guage to 12 guage?
joed 01-12-2011 09:56 AM
No reason to change the cable. You can use #10 cable for anything 30 amps or less.
Change the breaker. Install proper receptacle. Cap unused wire.
jbfan 01-12-2011 10:57 AM
You might have to pigtail a piece of #12 to fit onto the receptacle.
frenchelectrican 01-13-2011 12:52 AM
And make a note inside of the breaker box that you change the breaker size down to 20 amp so in case someone else not thinking and install the 30 amp breaker by mistake.
Merci.
Marc
michaelcherr 01-13-2011 10:14 AM
Does your current 220 have a ground? If not, I'm not sure if it's code acceptable to re-color the red as white. Seems safe though.
If it were me (and everything is accessable) I'd run a different 120v plug so you could in therory swap out a gas stove for electric and visa versa without any mods.
Ability to do gas or electric appliances helps resale of house.
AllanJ 01-13-2011 11:39 AM
It is not proper to put a different kind of plug on an appliance so you can continue use of the 240 volt receptacle in your 240 to 120 volt converted circuit.
All appliances have a maximum circuit rating even though the maximum current draw during usage is much less. The kind of plug "sorta" enforces this, for example a typical 2 prong plug is for 20 amp (or 15 amp) protected circuits.
You could pigtail a short 12 gauge wire at the panel end of this 10 gauge cable as an additional reminder not to use a 30 amp breaker.
RTypeEman 01-13-2011 01:15 PM
get one of these
http://www.dvinfo.net/forum/attachme...weradapter.jpg
joed 01-13-2011 01:20 PM
Put a stove receptacle in and use one of these. It is fused at 15 amps, so perfectly safe.
http://www.homedepot.ca/webapp/wcs/s...k=P_PartNumber
http://www.homedepot.ca/wcsstore/Hom...15752.17_4.jpg
jbfan 01-13-2011 03:33 PM
Is that something that is only sold in Canada?
Do they make a 4 wire type also?
Hourglass52 01-13-2011 06:23 PM
4 prong
If you look closely it is 4 prong.
Is it (UL) certified?
Plenty of house burning Chinese junk out there that isn't UL approved..
Bob
RTypeEman 01-13-2011 08:15 PM
according to the home depot link, it is CSA certified, which would be equivilent
Hourglass52 01-14-2011 04:44 AM
Duh
I was so hellbent looking for the "UL" I didn't see the CSA. DUH.
AllanJ 01-14-2011 09:38 AM
Originally Posted by joed (Post 569317)
Put a stove receptacle in and use one of these. It is fused at 15 amps, so perfectly safe.]
(picture above not requoted here)
Ah, a lot easier than building the portable subpanel myself piece by piece to plug into the existing stove receptacle.
Note that both of the gizmos mentioned higher up also require a stove circuit with a neutral.
Red Squirrel 01-14-2011 10:22 AM
I like the idea of either running a seperate 15 or 20 amp outlet and keeping existing plug, or that converter. As long as it's fused, and CSA approved that should be safe.
It's kinda like the outlets on an electric stove, they most likely have a 15 amp fuse inside the stove. At least I hope so.
frenchelectrican 01-15-2011 01:12 AM
Not with modern stoves I have ran into in both USA and French side I don't even see a fuse in there at all I know very old stove do have them for accesory recpetale but not with newer stove they got rid of that for safety issue.
Merci.
Marc