Old 10-08-2012, 10:15 AM   #31
Lic Electrical Inspector
electures's Avatar
Central air wiring question
Originally Posted by Glennsparky View Post
Thanks electures, I didn't know that. Do you have a code reference so i can study up?
The conductors from the panel to the AC disco are feeders since the disco contains overcurrent devices.
Feeder.
All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
215.3 Overcurrent Protection.
Feeders shall be protected
against overcurrent in accordance with the provisions of
Part I of Article 240. Where a feeder supplies continuous
loads or any combination of continuous and noncontinuous
loads, the rating of the overcurrent device shall not be less
than the noncontinuous load plus 125 percent of the continuous
load.
30A breaker requires #10 AWG. The conductors from the fused disco to the unit can be #12.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
Glennsparky (10-08-2012)
AC wiring question? Ralph III Electrical 4 03-04-2012 11:52 AM
Simple question regarding Wall Switch wiring kebrein Electrical 6 11-25-2011 08:54 PM
Landscape wiring question: GFCI and Breaker Amp MikeInDetroit Electrical 0 11-02-2011 10:43 AM
Low Voltage Wiring Question.. scyarch Electrical 3 10-23-2011 12:00 PM
central air unit question princessme HVAC 4 07-08-2006 10:13 PM