-   -   Central air wiring question (http://www.diychatroom.com/f18/central-air-wiring-question-159227/)
sgip2000 10-07-2012 01:22 AM
The old aluminum wiring for my A/C is oxidized and I'd like to replace it. Based on the info on the tag, I should be able to use a 30A breaker with 12 gauge or larger wire, correct?
Thanks.
http://i1337.photobucket.com/albums/...ps51733a0d.jpg
Dierte 10-07-2012 01:55 AM
No. size for your min breaker
Glennsparky 10-07-2012 04:10 AM
The OP is correct, that's the code. And for short distances there's no down side for #12 wire. For longer distances, esp. through hot attics, there is power lost as heat from the resistance in the wire. Upgrade the wire a little and you can recoup your investment with lower bills. By the way, aluminum is a perfectly good conductor. A wire brush, some Noalox grease and a torque screwdriver will make for efficient long lasting connections.
mpoulton 10-07-2012 04:55 AM
Totally incorrect. #12 on a 30A breaker is just fine in this application. In fact, I'm pretty sure #14 would be allowed since it is actually rated 20A (25A for 90C) but, like #12, is subject to a special maximum breaker size for most types of circuits - but not this one.
beenthere 10-07-2012 06:08 AM
12 is fine. Myself I would use a 10, but code allows 12.
darren 10-07-2012 08:56 AM
What are you talking about, if this was true he should be wiring it with #6 or #4 to save even more money.
hammerlane 10-07-2012 09:26 AM
:laughing::laughing::laughing::laughing:
sgip2000 10-07-2012 10:00 AM
Thank you. I do plan on using 10ga.
sgip2000 10-07-2012 10:03 AM
Thanks for your input. True, aluminum is fine, but since I have the copper, I'd like to just replace it.
electures 10-07-2012 11:57 AM
If you use a fused disconnect it has to be #10 to the disco, then #12 to the unit. Non fused can be #12 from the panel all the way.
sgip2000 10-07-2012 06:32 PM
I got it done with 10-2 to the fused disconnect and kept the 8ga whip that was already there.
Thank you everyone.
stickboy1375 10-07-2012 07:27 PM
Depending on what code cycle you are on, you could use #14 AWG. and a 30 amp breaker. :)
stickboy1375 10-07-2012 07:28 PM
Why would you use 10 AWG? It serves no purpose.
beenthere 10-07-2012 07:47 PM
No idea how long his run is. but less voltage drop on those hot days when the compressor has to start. Also, don't have to run a new wire down the road if he adds on and needs to increase the size of the A/C to something that has a min cir amp of 25.
No real cost difference between 10 and 12.
stickboy1375 10-07-2012 07:49 PM
yes, there is... :) I personally would wire the unit with 14 AWG.