Old 08-19-2008, 06:14 AM   #1
Central air unit throwing breaker
Our central air unit recently started to throw the breaker occasionally. Now it sparks if we reset. We've replaced the breaker but has not solved the problem. Any ideas on what to check next with the unit?
Thanks!
joycet is offline   Reply With Quote
Old 08-19-2008, 07:11 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Have an A/C guy out to check the condensor. The compressor is likely shot.
Old 08-20-2008, 12:15 PM   #3
J. V.'s Avatar
Faulty AC or wiring to the AC.
Old 08-20-2008, 03:11 PM   #4
If you replaced the breaker yourself you probably already have checked the condition of the wiring and connections in the panel and would be comfortable opening up the A/C disconnect box and checking all the connections and condition of wiring there. If all that looks good then check the wiring/connections in the A/C condenser itself. If all the wiring looks good then it sounds like the compressor and I'd have to punt to my HVAC guy.
Old 08-20-2008, 09:35 PM   #5
Electrician
SD515's Avatar
I agree with Pete. Could be the cooling fan motor, contactor, or the wiring inside the condensor unit, but it's been my experience that the culprit is usually the compressor. There is a quick, easy test to check for a compressor windings to ground short that your HVAC tech should be able to perform.
Central Air Trips Breaker RobSmith HVAC 6 08-05-2008 10:06 AM
Used Central Air Unit? shep28 HVAC 2 04-21-2007 08:59 PM
central air unit question princessme HVAC 4 07-08-2006 10:13 PM
Need to remove old central air unit pmb003 HVAC 4 05-03-2006 05:05 PM