#1 |
Carlon orange flexibla raceways?
Does anyone know if there are special restrictions for this product? I plan on running it in my unfinished basement to my garage to hookup a subpanel for my welder.
Thanks |
#2 |
You talking to me?
special like in...?
as with all materials, there are allowed installations and disallowed installations. |
#3 |
nap, i just had concern that since it isnt anywhere near as thick as grey pvc that there would be obvious different rules for how it is used.
#4 |
You talking to me?
yes, there is.
not sure exactly how you are using it but the two things that come to mind as possible concerns: not approved for direct earth burial, not acceptable where subject to physical damage. If you have access to an NEC, it is article 362. If you go to the electrical forums main section, I believe scuba dave has provided a link to access the NEC. |
#5 |
nap, i will be running 4 awg copper stranded from my main panel to my garage. The sub panel will be fed through a 2 pole 80 amp breaker. If i ran grey pvc there would be a lot of turns to get around my I beam and chimney on its way to the garage. Due to all the turns i am interested in running the flexible raceway. Does this sound okay? The wires in the raceway will be 3-4awg and one 6awg for ground.
#6 |
Nap i tried his link, it was broken. I did however order the newest copy and will be throughly reading it when it arrives. I wont be buring it and it shouldnt be damaged where i am runnign it.
#7 | |
You talking to me?
Carlon orange flexibla raceways?Quote:
a. for exposed work, where not prohibited by 362.12 b. Concealed within walls, floors, ceilings then, when you go to 362.12 Uses not permitted, it states (7) in exposed locations, except as permitted by 362.10(1) (and others) so, when does the merry go 'round stop? 362.12 says it is not permitted to be run exposed except as permitted in 362.10 and 362.10 says it is allowed unless prohibited by 362.12. You do need to understand that ENT is restricted to the same amount of bend between two junction boxes or pull points as PVC is. That is 360º. #8 would be acceptable for EGC. |
#8 |
Licensed electrician
I believe that the orange Carlon ENT is only for low voltage use. The blue can be used as a line voltage conduit, but is limited to interior usage only.
Answers based on the National Electrical Code. Local amendments may apply. Check with your local building officials. |
#9 | |
You talking to me?
I figured the OP knew what he has and it was ENT while in fact, it sounds like he has innerduct. so shawn, be sure you have ENT (that is the specific name it must be labeled with). If you don't, do not use it for regular wiring. Carlongo on down to page 11 |
#10 |
I forget about the grey ENT, most of the time I only see the blue.
| Display Modes | |
| Black/White/Orange wire...what to do with orange | Wingingit | Electrical | 9 | 06-23-2009 01:10 PM |
| orange peel when painting cabinets | ponch37300 | Painting | 8 | 04-16-2009 11:55 AM |
| Orange Peel Texture Help please | kalaniwavo | Painting | 10 | 05-25-2008 06:39 AM |
| Help! Our contractor made our kitchen cabinet door stain TOO ORANGE! | Nikki99 | Painting | 12 | 11-20-2007 12:45 AM |
| Same Ceiling: orange peel and knockdown | sir_rob | Painting | 17 | 10-01-2007 05:28 PM |
