Old 04-14-2009, 07:44 PM   #16
Licensed Electrician
Magnettica's Avatar
Rewards Points: 150
Send a message via Yahoo to Magnettica
This is a 115 volt system with a minimum ampacity requirement of 14 amps, and the overcurrent protection (circuit breaker) is required to be a maximum of 20 amps.
So, you need 14-2 wire from the panel to the condensing unit, and a single-pole 20 amp circuit breaker.
Without having read each post on this thread, the 4 wires going from the outside CU to the indoor air handler are for control wiring. They may, or may not be 115 volts.
Magnettica is offline   Reply With Quote
Old 04-14-2009, 08:32 PM   #17
Learning by Doing
Leah Frances's Avatar
You want 12 g with 20A breaker.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 04-14-2009, 09:33 PM   #18
dSilanskas's Avatar
You fried the unit if you hooked it up to 220volts. Its a 110volt system.... Sorry
dSilanskas is offline   Reply With Quote
Old 04-14-2009, 09:44 PM   #19
Licensed Pro
Minimum ampacity is 14A, so 14ga wire is appropriate. Max overcurrent protection is 20A, so 20A breaker is appropriate. HVAC units play by different rules.
To the OP.... can you return the unit as "defective out of the box"?
Old 04-14-2009, 09:54 PM   #20
Magnettica's Avatar
Rewards Points: 150
I tend agree.
Old 04-14-2009, 10:22 PM   #21
I will see tomorrow about being able to return the item. How "fried" is "fried"? I have access to the circuit board on the indoor unit and the 6.3 fuse is blown from what I can see. Would replacing the fuse work?
igotshocked is offline   Reply With Quote
Old 04-14-2009, 10:25 PM   #22
Electrical Contractor
jbfan's Avatar
Rewards Points: 482
It can't hurt to try and replace the fuse.
Old 04-14-2009, 10:25 PM   #23
dSilanskas's Avatar
Possible you can try.
Old 04-14-2009, 10:29 PM   #24
Will a AGC 2A work?
Old 04-14-2009, 10:34 PM   #25
jbfan's Avatar
Rewards Points: 482
Originally Posted by igotshocked View Post
Will a AGC 2A work?
Not long enough to see if it will run.
You need to replace the fuse with the same size and rating.
Old 04-14-2009, 10:41 PM   #26
I will go to radio shack tomorrow and see if they have one. Anything else I should check out that could have possibly blown and could pick up at radio shack as well?
I really hope that this will fix it...
Old 04-15-2009, 10:10 AM   #27
Ok, I went to the shack and bought a 6.3 fuse. Replaced the blown one in the indoor unit, turned breaker on, it beeps and blows at the same time.
Is there anything specifically that would cause this? Here is a link, both wiring diagrams are here for indoor and outdoor unit:http://www.ajmadison.com/ajmadison/i...lessManual.pdf
Is this thing shot? Am I just wasting my time? Or is this thing fixable?
Old 04-15-2009, 11:40 AM   #28
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Reading the diagram power enters the unit circuitry at the outdoor unit on the black wire connected to L. A brown jumper then connects L to L1 taking power to the indoor unit on the black wire. This gets power to the stepping motor, indoor unit fan motor and low voltage transformer.. When the unit powers up the NO switch at the indoor unit closes sending power over the red wire to power the outdoor unit compressor and condenser fan. The 6.3 amp fuse protects the stepping motor and indoor unit fan. The circuit breaker protects the outdoor unit along with the internal overload of the compressor. If the 6.3 amp fuse blows you have no low voltage control because the transformer cannot get power. Nor can the stepping motor and fan motor of the indoor unit run. Without control voltage I doubt the outdoor unit can operate on call for heat or cool because the NO switch probably closes on low voltage control.
So my guess is you likely need to see about what to do in returning the damaged unit. If you are responsible for overpowering the unit by connecting to 240 volts you are going to have to fess up the responsibility for damaging the unit IMO. This likely will require purchasing a new one. Live and learn. Connecting a 120 volt unit to 240 volts when it was obvious being wired to a double pole breaker would tell me that you should not have been attempting the electrical part of this install. I don't mean that in a insulting manner but it was a fundamental mistake. Just how I see things.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 04-15-2009, 11:48 AM   #29
Tool Geek
PaliBob's Avatar
Rewards Points: 2,160
Stubbie, Well Said, Good Analysis
Disclaimer
& Stay Safe
.....Bob Lavery
Old 04-15-2009, 02:17 PM   #30
Thanks for taking the time out to help me further understand whats going on with this unit. Also no affense taken, I assume all responsibility. I made the error of thinking that this compressor would easliy take the place of the one I was replacing.
Since hooking it up to the 240 volts blew the unit(s), does this mean that it just blew the circuit breaker (outdoor) as well as the 6.3 fuse (indoor)? Or does this mean that pretty much all electrical components on both units are shot? It seems to me that I should be able to just replace the circuit breaker and fuse, for that is what they are there for right?
I would hope that atleast one if not both, either outdoor or indoor unit is salvagable for the simple fact that this was an expensive purchase and hopefully I can save some money from the error I made.
Need Luxaire Forced Air Furnace Wiring Diagram misticvillage HVAC 7 04-15-2009 04:09 AM
Electrical Riser Diagram jaeht Electrical 7 02-21-2009 07:36 PM
Electrical SubMeter Wiring Help - Please. Jasondt2001 Electrical 50 01-07-2009 02:35 PM
outside unit kicks on, fan won't turn. Roger Nuss HVAC 9 07-20-2008 05:59 PM
Basic Switch wiring question; Dimmer to Toggle switch (Pictures included) inspectator Electrical 8 08-07-2007 01:19 AM