Can You Code A Green Wire For Hot? - Electrical - DIY Chatroom Home Improvement Forum
Old 01-07-2009, 02:54 PM   #1
They're all fixer-uppers
J187's Avatar
Rewards Points: 516
Can you code a green wire for hot?
At work, they are looking to run a 220 circuit through conduit 40'. They have a spool of 10awg green and they want to know if its possible to use green for the hot leads and tape them black and red at each end respectively? I know this is possible for white, but is green off limits?
J187 is offline   Reply With Quote
Old 01-07-2009, 03:29 PM   #2
Smaller than #4 is a code violation....unless they tape it the whole length.
Minor offense IMO. If I did it, I'd tape it cleanly/tight for about a foot then pull it back in the conduit a few inches (both ends).
220/221 is offline   Reply With Quote
Old 01-07-2009, 04:35 PM   #3
Violation of 250.119.
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section. Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors.
Spend the $90 for a 500ft spool of black, or buy 50' each of black and red by the foot at Home Depot.
Willis
williswires is offline   Reply With Quote
Old 01-07-2009, 04:37 PM   #4
Electrician
You are a beauty.
chris75 is offline   Reply With Quote
Old 01-07-2009, 04:42 PM   #5
J187's Avatar
Rewards Points: 516
Thanks guys.
Old 01-07-2009, 04:53 PM   #6
dSilanskas's Avatar
Minor offense?! Interesting
dSilanskas is offline   Reply With Quote
Old 01-07-2009, 05:11 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I'd be more worried if he said to tape it the entire length......
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 01-07-2009, 05:59 PM   #8
Rewards Points: 2,350
Nobody caught the part where he said he "knew" it was OK with white wire. It's only OK to recode a white wire in a cable, not conduit.
But, like 220 said, it's pretty minor, but I would only do it in a pinch. And I wouldn't use tape. I'd use something permanent like a sharpie. I once colored some gray #12 with a red sharpie, so about a foot at each end was red inside the pipe.
Old 01-07-2009, 07:10 PM   #9
The slick trick, if you had a bunch to do, is to take the old school fat magic marker and drill a small hole thru the felt tip. Run the wire thru and it's golden.
ANd yeah....you can't recode a white wire smaller than #4. I know I have never done it and I never will.
Old 01-07-2009, 09:47 PM   #10
Electrical Contractor
jbfan's Avatar
Rewards Points: 412
Me either!
jbfan is online now   Reply With Quote
Old 01-08-2009, 11:14 AM   #11
Rewards Points: 130
Do not use the green period. Get the right color. Tape comes off and markings can discolor over time. Use what green you have for the EGC.
Melted Service Entrance Wire in Panel theatretch85 Electrical 13 08-22-2008 10:37 AM
Hall light worked before installing a new light fixture in bathroom jcfan7 Electrical 40 02-23-2008 09:46 AM
Stranded wire on screw connections BigJimmy Electrical 7 01-19-2008 02:42 PM
Does a 6 x 12ga wire nut exist? peeks Electrical 1 10-02-2005 09:58 AM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 07:43 PM