At work, they are looking to run a 220 circuit through conduit 40'. They have a spool of 10awg green and they want to know if its possible to use green for the hot leads and tape them black and red at each end respectively? I know this is possible for white, but is green off limits?
220/221 01-07-2009 03:29 PM
Smaller than #4 is a code violation....unless they tape it the whole length.
Minor offense IMO. If I did it, I'd tape it cleanly/tight for about a foot then pull it back in the conduit a few inches (both ends).
williswires 01-07-2009 04:35 PM
Violation of 250.119. :no:
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section. Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors.
Spend the $90 for a 500ft spool of black, or buy 50' each of black and red by the foot at Home Depot.
chris75 01-07-2009 04:37 PM
You are a beauty. :yes:
J187 01-07-2009 04:42 PM
Thanks guys.
dSilanskas 01-07-2009 04:53 PM
Minor offense?! Interesting :laughing:
Stubbie 01-07-2009 05:11 PM
I'd be more worried if he said to tape it the entire length......:)
InPhase277 01-07-2009 05:59 PM
Nobody caught the part where he said he "knew" it was OK with white wire. It's only OK to recode a white wire in a cable, not conduit.
But, like 220 said, it's pretty minor, but I would only do it in a pinch. And I wouldn't use tape. I'd use something permanent like a sharpie. I once colored some gray #12 with a red sharpie, so about a foot at each end was red inside the pipe.
220/221 01-07-2009 07:10 PM
The slick trick, if you had a bunch to do, is to take the old school fat magic marker and drill a small hole thru the felt tip. Run the wire thru and it's golden.:thumbup:
ANd yeah....you can't recode a white wire smaller than #4. I know I have never done it and I never will.:jester:
jbfan 01-07-2009 09:47 PM
Me either!:thumbsup:
J. V. 01-08-2009 11:14 AM
Do not use the green period. Get the right color. Tape comes off and markings can discolor over time. Use what green you have for the EGC.