Can Type Nm-b Wire Be Used Outside In Conduit? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-25-2013, 04:45 PM   #1
Rewards Points: 170
Can type nm-b wire be used outside in conduit?
Can type nm-b (14-3) romex wire be used outdoors if placed in conduit to add additional receptacles to the back of a house/
diyer111 is offline   Reply With Quote
Old 05-25-2013, 04:55 PM   #2
Rewards Points: 6,652
Depends on your local ordinances. I personally wouldn't. If using all conduit outside, pull THHN/THWN instead of Romex.
Old 05-25-2013, 05:51 PM   #3
Rewards Points: 1,192
No. Romex+outside in conduit= wet location.
bobelectric is offline   Reply With Quote
The Following 3 Users Say Thank You to bobelectric For This Useful Post:
jbfan (05-26-2013), Philly Master (05-25-2013), sirsparksalot (05-31-2013)
Old 05-25-2013, 05:58 PM   #4
Semi-Pro Electro-Geek
Rewards Points: 2,970
Conduit which is not subject to any weather would be OK, but very few outdoor locations fit that description. The bottom line is this: if you could use NM there without conduit, then you could sleeve it in conduit. If you can't use NM there without conduit due to weather exposure, then adding conduit doesn't get you anything. The inside of a conduit in a wet location is a wet location.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 05-25-2013, 06:31 PM   #5
E2 Electrician
stickboy1375's Avatar
no......
The Following 3 Users Say Thank You to stickboy1375 For This Useful Post:
Kyle_in_rure (05-25-2013), Philly Master (05-25-2013), sirsparksalot (05-31-2013)
Old 05-25-2013, 08:01 PM   #6
Electrical Enthusiast
Rewards Points: 504
You would need to use UF cable, or most likely THHN/THWN Wires since you want to run 14/3.
Kyle_in_rure is offline   Reply With Quote
Old 05-25-2013, 09:08 PM   #7
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
NO ...
history in the making we all agree ...
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
The Following 3 Users Say Thank You to Philly Master For This Useful Post:
jbfan (05-26-2013), sirsparksalot (05-26-2013), stickboy1375 (05-25-2013)
Old 05-25-2013, 10:12 PM   #8
" Euro " electrician
frenchelectrican's Avatar
One thing over here it will be the same rules no NM cable on outdoor location as well only UF cable or THHN/THWN or SWA ( steel wire armoured cable ) is one of few most common allowed items we can use on outdoor useage over here in France.
Merci,
Marc
The Following User Says Thank You to frenchelectrican For This Useful Post:
Old 05-25-2013, 10:40 PM   #9
Pvc...sch 40 or 80(depends)....then thhn/thwn..... about 20 cents a foot..equals done right
Bobka is offline   Reply With Quote
Old 05-25-2013, 10:46 PM   #10
You can stub out NM to a outlet box or base plate for a light on the side of the house, and that is it. Otherwise, UF if going out any further than 8 inches from the side of the home, or THHN/THWN in conduit.
Old 05-25-2013, 11:37 PM   #11
Where did this 8 inch rule appear from?
Old 05-26-2013, 12:02 AM   #12
...the p*** industry
Old 05-26-2013, 12:02 AM   #13
Who says that it has to be a rule. There is this thing called common sense, which most of us use, when we do stuff. Six inches from the back of the box is allowable for giving you enough wire to attach a switch, outlet, or wire nut, but I just threw the eight inch statement out there, because as we say in my neck of the woods, "a little extra always helps, when doing something the right way."
If you have not realized, we are not code compliance officers, nor are we to enforce the codes of the areas that people live in, that post on here. We are just a group of people trying to have a round table discussion in what is best to do in a situation, and how to do it in a way, that it will not cause problems later on, if you either have to go and sell the place, due to not required to pull a permit to do the work, if your area does not require it, or if your area does require a permit, you have at least enough basic info, that you can take that and research further to find out exactly how to do it the way your AHJ wants it done.
Old 05-26-2013, 12:03 AM   #14
That does not even pass in that industry as allowable.
Old 05-26-2013, 12:05 AM   #15
jproffer's Avatar
Rewards Points: 716
But you're throwing hard numbers out there like it's written somewhere....and it's not.
jproffer is offline   Reply With Quote
Wire type for extensions to reach breakers broecher Electrical 17 10-25-2012 08:25 AM
THWN wire; Gray pvc Conduit; and GFCI receptacles Buzzy Electrical 29 09-26-2012 02:41 AM
What type of wire is this? hotot Electrical 5 09-22-2012 05:03 PM
Best way to add one more wire to an existing conduit miamicuse Electrical 15 05-29-2012 09:05 PM
Wiring nut type for lamp wire and ballast wire. Wek Electrical 3 03-01-2011 01:59 PM