Can A Square D 4 Pole Circuit Breaker Be Used As A 2 Pole Circuit Breaker. - Electrical - DIY Chatroom Home Improvement Forum
Old 08-23-2011, 09:43 PM   #1
Can a Square D 4 pole circuit breaker be used as a 2 pole circuit breaker.
I needed a 2 pole 200 amp breaker for my disconnect. My supplier sent me a 4 pole HOM2200u Square D 200 amp breaker. He told me it can be used as a 4 pole or a 2 pole breaker. Is this true?? I have never seen this done before...its always been my understanding that 4 pole breakers were for 3 phase. Can anyone shed some light on this???
TifcoJim is offline   Reply With Quote
Old 08-23-2011, 10:08 PM   #2
Code05's Avatar
Rewards Points: 1,104
I gotta do a little research on this breaker, I am pretty sure they sent you the wrong one. I will be back.
It is not a three phase breaker.
Code05 is offline   Reply With Quote
Old 08-23-2011, 10:58 PM   #3
Rewards Points: 6,652
It shows it as a Miniature 2 space breaker.
HOM2200 Circuit Breaker
Miniature Circuit Breaker Standard Type, 200A, 2-Pole, 120/240VAC, HOM, Plug-On
http://ecatalog.squared.com/fulldeta...number=HOM2200
eatures and Specifications
Mounting Type: Plug-On
Ampere Rating: 200A
General Application: Provides overload and short circuit protection
Approvals: UL Listed - CSA Certified
Circuit Breaker Type: Standard
For Use With: Homeline Load Centers
Voltage Rating: 120/240VAC
Depth: 2.98 Inches
Height: 3.13 Inches
Width: 2.00 Inches
Number of Poles: 2-Pole
Short Circuit Current Rating: 10kA
Space Required: 2
Type: HOM
Wire Size: #4-300 AWG/kcmil(Al/Cu)
Terminal Type: Screw
Old 08-24-2011, 12:59 AM   #4
" Euro " electrician
frenchelectrican's Avatar
There are couple verison of Homeline 200 amp breaker and the one you have with 4 pole type you can NOT use each one as two pole that is no way due you will trip it fast { the 4 pole will have 100 amp breaker each slot so you will have total of 200 amp per pole ( keep in your mind it is paired )
What the disconnect model number I can able look up to see what the correct breaker to use in that disconnect.
Unforetally C'est is not a 3 phase breaker at all if that was a three phase breaker you will have 6 pole verison of you describing.
again.,, post the disconnect model number we will go from there to assist you with proper one.
Merci,
Marc
running a subpanel from the main breaker on the pole. shocknawe Electrical 6 05-09-2011 10:51 AM
Square d breaker heatycooly Electrical 16 03-31-2011 07:37 PM
circuit breaker? blueandyellow Electrical 7 01-30-2011 11:27 PM
New circuit breaker owen22 Electrical 14 01-12-2010 08:08 PM
2 pole breaker Unregistered Electrical 3 09-11-2004 12:15 PM