Old 06-04-2012, 03:43 PM   #1
kmc
Can someone tell me why my low voltage lights are reading high current at the switch?
I'm trying to figure out if the problem is the way I'm measuring or possibly the transformer. I compared three different lines that each have two bulbs. Each line has it's own switch.
First line: I measure voltage at the wall switch which reads about 120.9 volts. Then I measure voltage at the led light sockets and it reads 12.1 volts from each of the two sockets on the line. So all is good at this point. Then I turn on the switch and measure current with my clamp ammeter at the switch and get 0.59 amps. So if I multiply 0.59 by 120.9 I get 71 watts. These are supposed to be 6.5 watt bulbs x 2 = 13 watts total. I then measure the current at the socket of the bulbs and get 0.41 amps. O.41 x 12.1 = 5 watts for each bulb.
Second line: If I duplicate the process again, I get 0.12 amps at the switch for the two bulbs there making the power consumption of each bulb about 7 watts. This is in the ballpark of what I want.
Third line: I measure current at the switch and it is again around 0.59 amps for the two bulbs or 71 watts.
Any ideas?
kmc is offline   Reply With Quote
Old 06-04-2012, 05:21 PM   #2
Semi-Pro Electro-Geek
First, your clamp-on meter is probably not very accurate at such low currents. Check the specs - it's probably good for something like +/-3% of full scale, which would likely be 40A or more. That's an allowable error of +/-1.2A.
But the real issue here is power factor. Measuring current and voltage separately allows you to calculate "apparent power" in volt-amps, but you do not know the phase relationship of the voltage and current waveforms. They are never perfectly aligned, and the phase shift between them results in less "real power" than the volt-amp calculation indicates. This difference is called the "power factor". Transformers that are under-loaded have very poor power factors, as do some electronic devices. So if the transformer for this lighting is rated for much more than the 13W load, you can expect the volt-amp measurement to be much higher than the real power being consumed. Similarly, if it's a cheap electronic lighting transformer, the power factor may be very low. To measure real power you need a wattmeter that accounts for the power factor.
mpoulton is offline   Reply With Quote
Old 06-04-2012, 06:41 PM   #3
A trick to make clamp on current meters more accurate for lower readings is to wind 10 turns of wire around the clamp and splice that into the circuit. Then divide reading by 10. You can do any number of turns that make sense,20, 30, ..... Just divide reading by the number of turns.
curiousB is offline   Reply With Quote
Old 06-04-2012, 08:34 PM   #4
Master Electrician
Any ideas?
What's the point?
brric is offline   Reply With Quote
Old 06-04-2012, 09:32 PM   #5
Are you using electronic transformers or iron cored trannys ?
dmxtothemax is offline   Reply With Quote
Old 06-04-2012, 10:38 PM   #6
JOATMON
ddawg16's Avatar
Just for clarification......
You have low voltage LED's that are being fed via a step down transformer? Or is it a solid state electronic transformer?
Are you sure that there is NOTHING else on the switches that feed the two lights? One way to confirm would be to measure the current going into the transformer....
Common Sense is like Deodorant. Those that need it the most don't use it.
My
and
4 way switch setup with multiple runs of lights CapeCod153 Electrical 23 03-28-2012 03:27 PM
Single Switch with Two 3-ways to Control 2 Separate Sets of Lights? LowlyDIYer Electrical 2 10-19-2011 10:11 AM
Help with wall switch - Constant voltage gambit023 Electrical 6 10-18-2011 10:30 PM
3-way illuminated switch - voltage present ktulu05 Electrical 18 11-29-2009 05:01 PM
Changing switch for lights in basement, confused on current wiring. RyanD Electrical 2 05-14-2009 09:37 PM