Can Somebody Point Me To The Tables For : - Electrical - DIY Chatroom Home Improvement Forum
Old 01-24-2012, 08:32 PM   #1
Doing it myself
Alan's Avatar
Rewards Points: 2,086
Can somebody point me to the tables for :
# of wires through certain size of hole
and
# of wires per box size
Please and thank you.
Journeyman Plumber
Old 01-24-2012, 08:48 PM   #2
Electrician
SD515's Avatar
Rewards Points: 504
# of cables in a hole drilled in a stud? I try to limit it to 3 cables of 14 ga or 12 ga in a 3/4" hole. Sometimes 4 but not too often.
Box fill can be found in section 314.16, and reference tables 314.16(A) & 314.16(B).
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
Alan (01-24-2012)
Old 01-24-2012, 09:02 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Bottom line on hole fill is, with cables #14, #12, & #10, you can have up to 9 current carrying conductors in almost any installation before derating is an issue. This means neutrals and hots, except for 3-wire home runs, which the neutral does not count as a CCC.
So...you can have up to eight cables in a hole before any derating is needed.
The Following 3 Users Say Thank You to Speedy Petey For This Useful Post:
Alan (01-24-2012), frenchelectrican (01-24-2012), SD515 (01-24-2012)
Old 01-24-2012, 09:06 PM   #4
Doing it myself
Alan's Avatar
So to clarify : the neutral and hot count as current carrying conductors, so each piece of 12-2 romex cable going through a hole counts as 2?
By that logic if I run a piece of 12-3 for some distance, that counts for 3 current carrying conductors?
Journeyman Plumber
Old 01-24-2012, 09:21 PM   #5
Yes.
No. The neutral of a 3-wire home run only carries the current imbalance, so it is exempted from being a CCC.
window condensation kmpittman Windows and Doors 4 11-29-2011 09:10 AM
Uneven floor and joists in new room Orangeclawhamme Building & Construction 35 11-16-2011 10:57 AM
sweating double pane windows etch Windows and Doors 6 10-31-2011 09:30 PM
Condensation amyevans Windows and Doors 6 10-21-2011 10:11 PM
Point of Entry Surge Suppression Question eltrigo Electrical 1 06-02-2005 06:14 PM