Can I Tie Two Breakers Together To Make A 240v Breaker? - Electrical - DIY Chatroom Home Improvement Forum
Old 03-25-2013, 08:43 PM   #1
Rewards Points: 948
Can I tie two breakers together to make a 240v breaker?
I know about how both sides of a 240v circuit must be off, or there will be voltage at a 240v device; but what is wrong with tying two 120v breakers together?
I assume it isn't allowed because a 240v breaker is 50% more than 2 120v breakers; but I have a bunch of 120vs and I need a 240v, so I am just wondering what the problem is.
Toller is offline   Reply With Quote
Old 03-25-2013, 08:52 PM   #2
Sparky
Rewards Points: 510
Factory 240v/2 pole breakers have internal common trip, something lacking from 2 handletied 120v/single pole breaker, therefore not allowed to be used in line to line applications
Techy is offline   Reply With Quote
The Following User Says Thank You to Techy For This Useful Post:
Kpack (03-25-2013)
Old 03-25-2013, 09:22 PM   #3
jproffer's Avatar
Rewards Points: 706
Maybe I'm the one misunderstanding...240.20(B)(2)
jproffer is online now   Reply With Quote
Old 03-25-2013, 09:27 PM   #4
Rewards Points: 13,270
The problum is you need a double poled breaker not two singles.
Old 03-25-2013, 09:54 PM   #5
jproffer's Avatar
Rewards Points: 706
I guess I'm misunderstanding then. Fair enough. Had the reference wrong...240.15(B)...
240.15 Ungrounded Conductors.
(A) Overcurrent Device Required. A fuse or an overcurrent
trip unit of a circuit breaker shall be connected in
series with each ungrounded conductor. A combination of a
current transformer and overcurrent relay shall be considered
equivalent to an overcurrent trip unit.
Informational Note: For motor circuits, see Parts III, IV, V,
and XI of Article 430.
(B) Circuit Breaker as Overcurrent Device. Circuit breakers
shall open all ungrounded conductors of the circuit both
manually and automatically unless otherwise permitted in
240.15(B)(1), (B)(2), (B)(3), and (B)(4).
(1) Multiwire Branch Circuit. Individual single-pole circuit
breakers, with identified handle ties, shall be permitted
as the protection for each ungrounded conductor of multiwire
branch circuits that serve only single-phase line-to neutral
loads.
(2) Grounded Single-Phase Alternating-Current Circuits.
In grounded systems, individual single-pole circuit
breakers rated 120/240 volts ac, with identified handle ties,
shall be permitted as the protection for each ungrounded
conductor for line-to-line connected loads for single-phase
circuits.
I understand the red section....manually and automatically (I.E. - internally and externally, yes?)...
Doesn't the blue section override that as "otherwise permitted in ......"
Not arguing, simply asking
Old 03-25-2013, 09:59 PM   #6
Sparky
Rewards Points: 510
you're correct, but the correct 'identified handle tie' will usually cost the same as or more than a standard current plug on circuit breaker.
I actually didn't know that exception was there, so i learned something today..
Old 03-25-2013, 10:02 PM   #7
jproffer's Avatar
Rewards Points: 706
Thought maybe I was missing something...that happens
Glad we got it cleared up.
That exception might be new in '11....not sure.
Old 03-25-2013, 10:04 PM   #8
Rewards Points: 948
Interesting...
I can buy a package of 3 approved handle ties for $5 and use some 120v breakers I have no use for, or buy a 240v for $18.
Have to chew on that one.
Old 03-26-2013, 11:48 AM   #9
Semi-Pro Electro-Geek
Rewards Points: 2,892
How many single pole breakers are rated 120/240V? Aren't "slash rated" single pole breakers fairly uncommon for residential panels?
EDIT: Nope, looks like almost all non-GFCI or AFCI breakers are slash rated. Is this exception a major change in the code? It looks like double pole breakers are no longer required in almost any residential application. A handle tie can be used instead. Weird.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 03-26-2013, 11:55 AM   #10
jproffer's Avatar
Rewards Points: 706
I have no idea how common they are. I was just throwing that code reference into the conversation.
Old 03-26-2013, 06:03 PM   #11
Sparky
Rewards Points: 510
exception exists at least as far back as the 2002 code.(240.20 prior to 08)
New 200 Amp Breaker box make noise speedster1 Electrical 3 12-02-2012 12:37 PM
Breaker panel with no main switch bjrsadie Electrical 13 11-17-2012 03:48 PM
GFCI Hot tub breaker nick26 Electrical 16 08-10-2012 08:48 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 12:36 PM
small voltage on circuit with breaker off jasonmechler Electrical 3 08-24-2009 09:52 AM