Can I Run 100amp Sub Threw 1" EMT? - Electrical - DIY Chatroom Home Improvement Forum
Old 11-11-2012, 03:11 PM   #1
Can I run 100amp sub threw 1" EMT?
I would like to add a 100amp sub panel for my air compressor (31amp) and a Furnace (6amp?). Is it possible to run this in 1inch EMT? What wire size would be required 4/6ga copper?
The reason I ask is I have the EMT all ready there. Just need to run wire about 20 feet.
rodm1 is offline   Reply With Quote
Old 11-11-2012, 03:50 PM   #2
Master Electrician
Rewards Points: 3,874
# 4 Cu is good for 85 amps, #3 Cu for 100amps. Using the emt as the equipment grounding, 1" emt will accomodate 3 #4 or #3 conductors per the NEC.
brric is online now   Reply With Quote
Old 11-11-2012, 04:24 PM   #3
Electrical Contractor
kbsparky's Avatar
I've installed a 100 Amp feeder consisting of (2) #3 hots, 1 #4 neutral, and a #8 ground (all THHN Copper) into a 1" conduit. Tight, but it fits, and legal.
-KB
Old 11-11-2012, 04:26 PM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,216
Why 100 amp for that load. Run #6 for a 60 amp sub and make the pull a lot easier (and cheaper) .
Coastal South Carolina
Old 11-12-2012, 04:51 PM   #5
Yes over kill, I think I'm going to use a 60amp service.