Can I Mix Conduit And Romex - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 02-05-2012, 10:53 AM   #16
Rewards Points: 1,010
Originally Posted by zappa View Post
True, just using all 600 volt wiring is the easiest way but there seems to be some misunderstanding with the voltage ratings in the same conduit. First, bare wire has no voltage rating, it is the insulation that gives it a "voltage rating".
300.2 Limitations.
(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 600 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
So I stand by my original post in saying that the OP is code compliant by using wire of different voltage ratings as long as ALL wires are listed above the maximum voltage.
I don't think anyone was arguing with you
Anti-wingnut is offline   Reply With Quote
Old 02-05-2012, 12:55 PM   #17
Rewards Points: 3,256
Far from an argument, just wrong information. I wasn't going to post again because it's not that big of a deal safety wise, but another poster asked specifically and was given the wrong information. I'm not going to go back and quote the posts but most think that all of the wires have to have the same voltage rating but that is not the case.
If the OP has a roll of 150 volt rated wire that he wanted to use for his alarm circuit he would feel that he can't use it because of the information that was given.
This is an electrical forum and I feel that the information should be accurate for safety and knowledge.
zappa is offline   Reply With Quote
Old 02-05-2012, 02:06 PM   #18
US ARMY RETIRED
ACR_SCOUT's Avatar
Question
I think just a couple more questions.
I went to the local box store. The stranded wire they have had THW printed on it not THWN. Is this the same stuff?
Is there a romex strain relief fitting to use with a plastic PVC box?
What the person at the store showed me was to use a metal box with a standard metal romex strain relief fitting for the romex feed. Then in order to adapt to the PVC conduit he said to use a pvc terminal adaptor such as pictured below with a locking nut. Is this normal?
ACR_SCOUT is offline   Reply With Quote
Old 02-05-2012, 02:25 PM   #19
Julius793's Avatar
Ok I'll take the blame, However I'm still under the impression that if the wires were class 2, then no matter the insulation ratings they wouldn't be allowed in the same conduit.
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 02-05-2012, 02:36 PM   #20
I'm not familiar with THW but a quick search indicated that the smaller gauges are solid wire and rated at 75C vs. stranded and 90C. I would feel better if someone else answered the THW question.
I do know that you will need to use different colors.
And I like the metal box and adaptor.
Old 02-05-2012, 11:48 PM   #21
Rewards Points: 264
acr_scout,
THWN is just the most common wet rated wire found in the big box stores. You can actual use any wire with the following ratings:
MTW, RHW, RHW-2, TW, THW, THW-2, THHW, THWN, THWN-2, XHHW, XHHW-2, ZW (NEC 310.10 (C))
I don't recall seeing a romex strain relief fitting for the PVC boxes.
I do suggest using either a metal box or a standard plastic junction box, and not one of the PVC conduit boxes. The PVC conduit boxes have significantly thicker walls and standard fittings won't grab on to them very well.
a_lost_shadow is offline   Reply With Quote
Old 02-06-2012, 06:12 AM   #22
300.2 Limitations.
So does this mean that in the same conduit, you can run say #6 240v 30amp, #12 120v, 20 amp and say #14 24v 2amp as long as it say THWN rated at 600v.
Hardway is offline   Reply With Quote
Old 02-06-2012, 08:25 AM   #23
The short answer is yes, but this section relates to insulation ratings only. To make it more clear, your 24 volt circuit could also use wire that is rated 240 volts or higher because 240 volts is the highest in the conduit.
The long answer which doesn't relate to this section is what kind of low voltage signals can be run in the same conduit. There are many exceptions and limitations all throughout the code that addresses this subject.
Old 02-06-2012, 08:33 AM   #24
ok thanks just want to make sure i was understanding it.
Old 02-06-2012, 09:58 AM   #25
Julius793's Avatar
So to stir things up a bit what class circuit does your float switch fit into??
Old 02-07-2012, 09:50 AM   #26
Julius793's Avatar
Can u post the transformer specs that you plan on powering the float switch from?
Old 02-07-2012, 09:56 AM   #27
US ARMY RETIRED
ACR_SCOUT's Avatar
Well I've desided to go a different route. I am only running power to the pump tank. The tank will have a combined pump control and alarm. Hence I only need to run power.
Old 02-07-2012, 10:02 AM   #28
Julius793's Avatar
That's good because chances are you would not be able to put them in the same conduit.
Old 02-07-2012, 10:08 AM   #29
US ARMY RETIRED
ACR_SCOUT's Avatar
Can is a question of ability. I am sure I'm able. Legal is completely different.
Old 02-07-2012, 10:22 AM   #30
Julius793's Avatar
Correct but you didn't come here asking if you have the ability!!
Tags
alarm , septic , septic control
Joining romex and conduit Restyle Electrical 2 11-08-2011 03:01 PM
loose Romex entering EMT conduit inside ceiling amakarevic Electrical 6 11-02-2011 09:32 PM
loose Romex into plastic conduit box amakarevic Electrical 4 06-30-2011 09:27 PM
Use of unsheathed Romex NM-B wires in conduit? WoodworkerDave Electrical 10 09-29-2008 05:57 PM
Cost Difference Between Conduit & Romex Shawns4 Electrical 39 08-25-2008 05:01 PM