Can I Mix Conduit And Romex - Electrical - DIY Chatroom Home Improvement Forum
Old 02-05-2012, 07:47 AM   #1
US ARMY RETIRED
ACR_SCOUT's Avatar
Question
Can I mix conduit and romex
Hello all.
I am working on a septic Alarm project (I currently don't have an alarm).
I have become convinced that PVC conduit from the house to the septic pump tank is the best way to go. In that conduit, as I understand it, I want to run #12 stranded THHN. So for power to the pump the wires will be one black, one white, and one green. (The pump is 110/20 amp half horsepower)
Because I am thinking about keeping the alarm inside the basement, I will need to also run wires through the same conduit for the alarm float switch. What color and size wire should these be?
Finally, here is the hard question. From the main service panel to the point of penetration for the conduit is ~20 feet. What I would like to do is run #12/2 with ground romex. In the junction box at the point where the conduit penetrates the wall I would like to put a plug for the alarm.
So here is what would be in the junction box.
1-plug
splices going from romex to stranded THHN
2 wires passing through for the alarm float switch
Is any of this legal (VA, USA)?
Otherwise I will buy an external alarm and pump control panel. Run romex from main service panel to a junction box. Switch to stranded THHN for the run inside the pvc conduit which goes to the septic control panel at the septic pump chamber.
Thank you,
Fred
ACR_SCOUT is offline   Reply With Quote
Old 02-05-2012, 07:58 AM   #2
Julius793's Avatar
What's the voltage of the float switch?
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 02-05-2012, 08:22 AM   #3
Rewards Points: 6,652
I see no problem doing it that way.
Old 02-05-2012, 08:33 AM   #4
Rewards Points: 3,256
I agree, but if the float switch is low voltage make sure the wiring going to it is rated as high or higher than 120 volts.
zappa is offline   Reply With Quote
Old 02-05-2012, 08:39 AM   #5
joed's Avatar
Rewards Points: 13,748
As long as you use the same thwn rated wire you are using for the pump no problem running them in the same conduit, not matter what the voltage. It's the insulation rating of the wire that is important. Use any colour you wish except for green for the alarm.
No problem with the junction box either.
Old 02-05-2012, 08:49 AM   #6
joed, let me make sure I get this one right. You can run mixed voltage in the same conduit as long as the wire has the same rating, to match the highest voltage/amps?
Writer’s information is for discussion purpose only and should be confirmed by an independent source.
Hardway is offline   Reply With Quote
Old 02-05-2012, 08:55 AM   #7
Electrical Contractor
jbfan's Avatar
Rewards Points: 650
That is correct.
The lowest voltage wire has to have the same rating as the highest voltage wire.
Old 02-05-2012, 08:58 AM   #8
Originally Posted by jbfan View Post
That is correct.
I know these things, just can't remember why anymore.
Old 02-05-2012, 09:00 AM   #9
joed's Avatar
That is correct. Also note that wire being underground must be THWN rated. It was stated as THHN in the original post. However most THHN is also rated THWN. Just make sure it is dual rated.
Old 02-05-2012, 09:01 AM   #10
jbfan's Avatar
Rewards Points: 650
I usetacould do things I can't do now
Old 02-05-2012, 09:17 AM   #11
yes I know this thanks.
Old 02-05-2012, 09:21 AM   #12
Yeah I know this feeling too. I used to be able to jump fences fast, I still can. Just slower, because now if I fall I lay there for awhile before I get up.
Old 02-05-2012, 09:52 AM   #13
True, just using all 600 volt wiring is the easiest way but there seems to be some misunderstanding with the voltage ratings in the same conduit. First, bare wire has no voltage rating, it is the insulation that gives it a "voltage rating".
300.2 Limitations.
(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 600 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
So I stand by my original post in saying that the OP is code compliant by using wire of different voltage ratings as long as ALL wires are listed above the maximum voltage.
Old 02-05-2012, 10:24 AM   #14
US ARMY RETIRED
ACR_SCOUT's Avatar
It still must be THWN even in conduit?
Old 02-05-2012, 10:37 AM   #15
Yes absolutely...conduit is considered a wet location. Most THHN is also listed as THWN. I'm not sure you could still find THHN only.
Tags
alarm , septic , septic control
Joining romex and conduit Restyle Electrical 2 11-08-2011 03:01 PM
loose Romex entering EMT conduit inside ceiling amakarevic Electrical 6 11-02-2011 09:32 PM
loose Romex into plastic conduit box amakarevic Electrical 4 06-30-2011 09:27 PM
Use of unsheathed Romex NM-B wires in conduit? WoodworkerDave Electrical 10 09-29-2008 05:57 PM
Cost Difference Between Conduit & Romex Shawns4 Electrical 39 08-25-2008 05:01 PM