Hi,
I had an electrician rewire my house recently, but he made a mistake in wiring for a gas, not an electric dryer.
It's wired for 220V 20amp (12 gauge wire), but my dryer say it needs 23amps on the side door (which is a standard 30 amp dryer due to the 80% code requirement).
My question: what might I expect if I swap the power chord to take a correct plug for the 220V, 20amp socket and run my dryer at 3 amps below it's stated need?
Is this safe? Will it damage the equipment or make the dryer less functional?
Thanks to anyone who can help!
Alan
uncle al is offline   Reply With Quote
Old 12-20-2011, 03:39 PM   #2
Electrician
Rewards Points: 760
If it is 10 gauge and there is 4 wires(smart electrician if he did this) then you would have to swap the plug and the breaker out. I would call your electrician and see what he did.
Was your typo the gauge of wire. Also 80% has nothing to do with this, that is for continous loads and your dryer is not considered continous. If they made a 24A breaker you would be able to use it for your dryer. Dryers are 30A because most dryers require 23-25A and the next standard breaker size is 30A.
darren is offline   Reply With Quote
Old 12-20-2011, 03:43 PM   #3
Jack of all - master none
hyunelan2's Avatar
Rewards Points: 682
What will likely happen, is you are going to trip your breaker as the dryer tries to pull more power than the breaker allows.
What you need to do is change the breaker and outlet to work for 30a. I think #10 wire is good for 30 amps, though I may be mistaken - wait for an electrical guru to reply. Are you sure it is 10 gauge wire in there?
hyunelan2 is offline   Reply With Quote
Old 12-20-2011, 03:43 PM   #4
Hey Darren,
Thanks for the response. I made a mistake when I was writing the initial post. We confirmed that it's 12 gauge, not 10. Thanks for your advice.
Alan
Old 12-20-2011, 04:09 PM   #5
Electrician
Rewards Points: 760
You will have to get some 10/3 over to the dryer location. Did you pay your electrician to run 10/3 for your dryer, if so he should come back and make it correct at no charge.
Old 12-20-2011, 04:11 PM   #6
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
The dryer will still draw the 23 amps and it will hopefully trip the 20 amp breaker. You run the risk of the conductor overheating and causing a fire. Assuming this is a made for the US dryer, you need a 240/120 volt, 30 amp, 3 wire circuit with 10/3 cable (or equal in conduit).
BTW, a dryer is not a continuous draw appliance and is not covered under the 80% requirement.
Coastal South Carolina
Old 12-21-2011, 10:35 AM   #7
Rewards Points: 718
you need to change wire and breaker, but i actually had on another house a 23A dryer and a 12ga and 20 amp breaker for years and it has never trip (was a sqd breaker not FPE). dryer was really taking 23A (read with clamp on)
carmusic is offline   Reply With Quote
Old 12-21-2011, 03:13 PM   #8
Interesting...
One option on the table is to switch the cord and install a 30amp circuit in the circuit breaker so that it doesn't trip, but use the 12g wire. Does this present a fire hazard?
Another option might be to hook up the dryer with a different power cord, but not change anything on the panel, then it would either trip the circuit or, if not, we could maybe get away with this?
Thanks for all the advice thus far, and let me know your thoughts.
Alan
Old 12-21-2011, 03:45 PM   #9
Electrical Contractor
jbfan's Avatar
Rewards Points: 138
Neither option is code complaint.
The only option you have is do it right.
Change the wire from the panel to 10 gauge and replace the breaker with a 30 amp and install the dryer to code.
Another Dryer Question 3 to 4 wire John3rd Electrical 15 07-29-2015 02:10 PM
washer plugs into dryer, but amps on plugs don't match nmliz Electrical 22 10-19-2011 06:39 PM
Removed basement stairs - put in floor for washer and dryer capslock Flooring 3 10-09-2010 03:15 PM
Please look at this dryer vent installation Andy Griffith Appliances 6 08-31-2009 01:39 PM
Dryer Grounding??? Traci_howdyadothat Electrical 7 05-27-2008 02:14 PM