Can I Have GFCI Outlets On Same Circut As Normal Outlets? 12/2 - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-07-2013, 07:53 AM   #16
Rewards Points: 150
Originally Posted by Philly Master View Post
NOT TRUE !!!
Section 220-3(c)(6). The NEC does not have a specific rule that says 10 receptacles on a 15 ampere circuit or 13 receptacles on a 20 ampere circuit. For 15 ampere circuits, the calculation is as follows: 120 volts x 15 amperes = 1800 VA/180 VA = 10 receptacles, and for 20 ampere circuits, 120 volts x 20 amperes = 2400 VA/180 VA = 13 receptacles.
I would suggst you get a copy of Mike Holts book on calculations it will help clear up your confusion.
usair is offline   Reply With Quote
Old 05-07-2013, 08:27 AM   #17
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
Originally Posted by jbfan View Post
220.14(J)
Outlets specified in (J)(1),(2), and (3) are already included in the general lighting load of 220.12. No additional load calculations shall be required for such outlets.
As many receptacles as you would like to have on a general use circuit in residential.
as someone else said this is to calculate the SERVICE Conductors and OCP of the service .... now that we have moved to the interior of the house we must now use calculations for the individual branch circuits ...
2000 sp ft house ... @ 3 va ....6000 va lights and oultets ....
use 15 amp circuits = 4 circuits (3.33) for all the outlets and all the lights ( general purpose )... ( 1800 va / 6000 va ) REALLY ??? LMAO
so IMHO ... this still stands on the "INDIVIDUAL BRANCH CIRCUIT"
[220.14(I)]. Except as covered by 220.14(J) and 220.14(E)—dwelling occupancies and banks/office buildings, respectively—the minimum is 180VA for each single or multiple receptacle in one yoke. But if a single piece of equipment consists of a multiple receptacle comprised of four (or more) receptacles (four example, a four-gang receptacle box or strip), then the minimum is 90VA per receptacle. This means, for example, you would allow 180VA for a duplex receptacle unit but 360VA for a four-gang receptacle unit.
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 05-07-2013, 08:28 AM   #18
Rewards Points: 516
220.14(J)
Yes LOAD but LOAD of WHAT ??? ie the SERVICE NOT the BRANCH CIRCUIT ...
Old 05-07-2013, 09:08 AM   #19
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
NOT TRUE !!!
What version NEC are you getting this from? Does not exist in the 2011 NEC.
As for the number of receptacles on a circuit, there is no limit. The only requirement is;.
One 15A general lighting circuit for every 600 sq ft of living space, or
One 20A general lighting circuit for every 800 sq ft of living space.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following 3 Users Say Thank You to electures For This Useful Post:
jbfan (05-07-2013), Jim Port (05-07-2013), mm11 (05-07-2013)
Old 05-07-2013, 09:12 AM   #20
Rewards Points: 516
http://www.mikeholt.com/technical.ph...0through%20240
Old 05-07-2013, 09:39 AM   #21
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 5,408
Originally Posted by AllanJ View Post
There are some restrictions on what branch circuits can serve what, but a circuit serving bedrooms may also serve an outide deck.
Depending on the exact wiring, optionally one ground fault interrupter unit can serve both deck receptacles.
To accomplish the latter, one of the outlet boxes must be downstream of the other in the usual daisy chain and also the circuit must not be a multiwire branch circuit typically using red and black hot wires sharing the neutral. Install the GFCI unit in the more upstream of the two outlet boxes and connect both black and white of the continuing cable to its "load" terminals instead of wire nutting pigtails to the "line" terminals.
In order to continue GFCI protection downstream from a GFCI receptacle (load terminals) on a MWBC that also continues, you need to run a separate 2 conductor cable for the protected subcircuit.
You can have any number of separate GFCI units on the MWBC, connected via their line side terminals (subject only to the limit of total number of units or devices of all kinds).
(rarely seen) When the MWBC breaks into two (non-MWBC) subcircuits at a box, you would need a third subcircuit for continuing the GFCI protection if you also want both halves of the MWBC to continue downstream without protection.
The GFCI load side neutral and the line side neutral may not be bonded together (interconnected using any combination of wires or components). Same for the load side hot and any line side hot.
Thanks Allan..... I agree. I was just confused by what you meant in the first post.
Best Peter
MTN REMODEL LLC is online now   Reply With Quote
Old 05-07-2013, 09:45 AM   #22
electures's Avatar
That is not NEC. It is from a practice exam.
Old 05-07-2013, 06:47 PM   #23
Licensed electrician
Rewards Points: 1,020
The answer to the original question does not require any calculation to be done.
The Following 2 Users Say Thank You to Jim Port For This Useful Post:
al_smelter (05-08-2013), MTN REMODEL LLC (05-07-2013)
Old 05-07-2013, 07:17 PM   #24
Rewards Points: 516
all the answers are from the NEC ....
Old 05-07-2013, 09:22 PM   #25
electures's Avatar
This is not a valid NEC section. It does not exist.
Again, where?
Old 05-07-2013, 09:55 PM   #26
Sparky
Rewards Points: 510
the most current NEC that 220-3(c)(6) exists in was the 1996 edition.
(6) Sign and outline lighting ............... 1200 volt-amperes
for each required branch circuitspecified in Section 600-5(a).
Techy is offline   Reply With Quote
Old 05-07-2013, 10:21 PM   #27
Rewards Points: 6,652
NOT TRUE !!!
Maybe in Canada or elsewhere, but not here in the U.S.. You could have a hundred outlets, or even a thousand outlets on a branch circuit, and you are not breaking any rules.
Just that you cannot plug in a hundred devices or a thousand devices into those outlets, unless they meet the 80% rule for amperage of the circuit, when all added together.
Old 05-07-2013, 10:22 PM   #28
:slam:
Old 05-08-2013, 04:59 AM   #29
jproffer's Avatar
Rewards Points: 702
NOT TRUE !!!
I didn't catch this until I saw it at least dozen times...
In this case, this code citation is absolutely true, although old lol...the NEC does NOT have a specific rule............
jproffer is offline   Reply With Quote
The Following User Says Thank You to jproffer For This Useful Post:
Philly Master (05-08-2013)
Old 05-08-2013, 08:41 AM   #30
Rewards Points: 516
Again, where?
Most of it is in the 2008 NEC HANDBOOK or what some refer to as the illustrated guide page 116 ...now the link I provoed was more than likely from 2005 or older... But that is where the "exhibits" come from The NEC ....
It would NOT behoove Mr. Holt or anyone else to teach stuff not covered in the NEC for test taking purposes ...
Piggy Backing Off GFCI Outlets miamicuse Electrical 20 06-05-2012 10:55 PM
Breaker Panel Replacement Plan jillers Electrical 24 01-28-2012 11:12 AM
OK to run one GFCI + 4 standard outlets from a junction box? Fulg Electrical 6 12-05-2010 12:43 AM
GFCI Outlets in Basement helpless handyman Electrical 4 04-20-2008 11:23 PM
two GFCI outlets at bath vanity Hickory Electrical 6 12-18-2005 10:31 AM