Can I Get Away With It? - Electrical - DIY Chatroom Home Improvement Forum
Old 12-06-2010, 05:07 PM   #1
can i get away with it?
So i have posted before about how i am putting a subpanel in my garage for my welder. The garage is attached and about 50 feet from the main panel. I have already run the wiring 3awg copper wire through hard plactic conduit where it is exposed in the basement and flexible blue ent where it runs unexposed along the i-beam. In my main panel i have it hooked up to a 80amp 2pole breaker. I have not bought the subpanel yet and was wondering since most box stores sell panel kits that already come with breakers can i buy a 100amp panel and use the 100amp main breaker in the new panel as a cutoff switch for the subpanel? The breaker in the main is 80amp protecting the wiring from going over its rated ampacity. Im trying to avoid having to buy another 80amp breaker.
1982shawn is offline   Reply With Quote
Old 12-06-2010, 05:20 PM   #2
I ask the impossible!
Rewards Points: 704
I'm hoping somebody will correct me if I'm wrong on this, but my understanding is that for the sub-panel you could get a main lug panel which doesn't have a main breaker (or you can use a panel that can take a main breaker and use it in this manner) and you just connect your feeder wires directly to the bus bars. This was something I was figuring out in planning for a subpanel I'll be installing soon.
WillK is offline   Reply With Quote
Old 12-06-2010, 05:26 PM   #3
Will you can use a main lug for this. I want a disconnect and the sub though. My main concern is can i use a breaker in the sub larger than the one in the main?
Old 12-06-2010, 05:29 PM   #4
By the one in the main i mean the breaker feeding the sub.
Old 12-06-2010, 05:31 PM   #5
Yes you can use the 100a panel with the 100a breaker
That is what I did in my pool cabana sub
You can only use a main lug in a detached structure if you have less then 6 breakers to shut everything off
....some Inspectors may require a main shut-off/breaker ahead of a panel that can have more then 6 breakers installed
OR
have a min shut off before the panel
Old 12-06-2010, 05:34 PM   #6
Scuba can i use a 100amp breaker and box if its feed by an 80amp breaker?
Old 12-06-2010, 05:35 PM   #7
Nothing past the 80 amp breaker in the main panel will be rated above 80 amps.
Old 12-06-2010, 05:40 PM   #8
Electrical Contractor
jbfan's Avatar
Rewards Points: 552
Yes!....
The Following User Says Thank You to jbfan For This Useful Post:
Scuba_Dave (12-06-2010)