-   -   Can I feed 1/2 a MWBC from a combination arc fault interrupter(CAIF) breaker? (http://www.diychatroom.com/f18/can-i-feed-1-2-mwbc-combination-arc-fault-interrupter-caif-breaker-153372/)
crankcase 08-11-2012 10:51 PM
If I'm reading my instruction sheet correctly my QO 15A CAIF it will trip instantly for a shared neutral. Does that mean that I am not allowed to use it to feed 1/2 of a MWBC?
k_buz 08-11-2012 11:00 PM
That is correct...and one of the huge downfalls of AFCI's. Although some manufacturers are starting to produce 2 Pole AFCI breakers. I think Siemans is one and I forget the other one.
crankcase 08-11-2012 11:18 PM
Thanks, I didn't realize it right away. Going to have to run those 2 a little different then.
kbsparky 08-12-2012 06:10 AM
Originally Posted by k_buz (Post 986544)
... I think Siemans is one and I forget the other one.
Cutler-Hammer comes to mind ....
stickboy1375 08-12-2012 11:13 AM
12 Attachment(s)
Square D makes 2pole AFCI's.... QO style too. :)
k_buz 08-12-2012 11:15 AM
Link? A quick Google search did not provide any matches.
stickboy1375 08-12-2012 11:19 AM
12 Attachment(s)
I cant find a link either, but Im almost positive we just did a job with a panel full of them.
I will verify this on monday... Sq D's website is pretty bogged up....
Jim Port 08-12-2012 12:08 PM
I thought Cutler was one of the few making a 2 pole AFCI.
k_buz 08-12-2012 12:11 PM
I have found CH and Siemans. This is the interesting thing, the code has been around for a long time now and only two types have been produced and nobody has came out with a listed AFCI receptacle. Why? Seems like the code is ahead of the technology.
stickboy1375 08-12-2012 12:27 PM
12 Attachment(s)
AFCI receptacles would be a sweet deal, and fix the multiwire branch circuit issues... Of course, I just rough in with 14-2-2 or 12-2-2.. so it's a non issue for me.
k_buz 08-12-2012 12:32 PM
The problem with AFCI receptacles is you have to meet a number of criteria to install them.
From 2011
Exception No. 1: If RMC, IMC, EMT, Type MC, or steel
armored Type AC cables meeting the requirements of
250.118 and metal outlet and junction boxes are installed
for the portion of the branch circuit between the branchcircuit
overcurrent device and the first outlet, it shall be
permitted to install an outlet branch-circuit type AFCI at
the first outlet to provide protection for the remaining portion
of the branch circuit.
stickboy1375 08-12-2012 12:34 PM
12 Attachment(s)
From 2011
Im betting there is no market place for the device, meaning, too expensive to produce for such little demand. I could be off on this of course. Not sure as a manufacture I would invest in this product though.
