Hi, I live in rural Panama, where I have a small house that is about 2000 ft away from the nearest transformer. Unfortunately the electrical company will not run a secondary electrical line up the road for me. I was on a budget when I installed the wiring, so I have 220V #6AWG aluminum cables running this distance, which I know is a long ways for this size wire. As I only have a few light bulbs and a small fridge, this hasn't been a problem, and I've had this set up for 2 years without incident. I do notice that the electrical system is taxed when the fridge's compressor clicks on (the lights in the house get very bright, I'm assuming this is an amperage spike to make up for the voltage drop).
However, I recently installed a pressure-tank system that draws water from an above-ground storage tank and pumps it into the house. The system uses a 1/2HP, 110V centrifugal pump to send water into the pressure tank and beyond into the house. The pump clicks on and off with a pressure switch. However, due to the electrical, occasionally the pump doesn't start well. I have notice that if I throw the breaker, and run out to the pump, I am able to get it going by spinning the fan on the back of the pump. Once I do that, it (mostly) starts and stops just fine with the pressure switch. However, if it sits too long and cools down, it generally needs to be helped again to start.
I'm worried that I (or someone else) will burnout the pump (or worse) at some point when they open the tap and don't realize it's trying to start. Is there a way to wire a capacitor to the pump to assist with the large current demands when the motor starts? I think this would solve the problem.
Thanks for your tips!
Drew in Panama
machodelmonte is offline   Reply With Quote
Old 03-23-2012, 06:57 AM   #2
Rewards Points: 826
Sounds like starter windings and or starter cap isn 't working
This isn't normal. I'd fix that first
curiousB is online now   Reply With Quote
Old 03-23-2012, 07:37 AM   #3
joed's Avatar
Rewards Points: 13,284
Lights getting brighter is the classic symptom of a loose neutral connection. Check all your connections between the POCO feed and your main panel. Have the POCO check theirs as well, including in the meter pan.
Old 03-23-2012, 08:37 AM   #4
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
If its not a cap start motor i wouldnt add one
"facts" have no relevance to this discusion
Posting from a concrete bunker under a non descript barn
plummen is offline   Reply With Quote
The Following User Says Thank You to plummen For This Useful Post:
zappa (03-23-2012)
Old 03-23-2012, 10:22 PM   #5
Idiot Emeritus
Rewards Points: 1,492
I doubt if the pump has any problem at all. 2000' of #6 AL causes too much voltage drop.
#6 AL is 0.8Ω per 1000'. 2000' out and 2000' back = 3.2Ω.
The resistance of both the start and run windings of a typical 1/21HP 120 volt motor would be less than 1Ω. this means that most of the voltage is dropped across the incoming wiring, leaving very little for the motor. There's a lot more than simple math to the equation, but I'd guess the motor is trying to start on about 40 or 50 volts.
If possible, change the motor to 230 volts. It'll still have greatly reduced voltage at startup, but it'll very likely start.
Also, I don't think the lights getting brighter is a loose neutral, I think it's because of the length of the wire.
2000' is a LONG way to push 120 volts, heck it's a long way for 480.
Rob
micromind is offline   Reply With Quote
The Following User Says Thank You to micromind For This Useful Post:
plummen (03-24-2012)
Old 03-26-2012, 09:18 AM   #6
Hey Rob,
Thanks for this, I did check the neutral and it wasn't loose - seems the most logical that it is just the distance. I found a cheap 220V 1/2 HP pump, I think I'm going to buy this one and give it a shot.
Eventually I'll need to rewire with thicker gauge, or get the power company to put an extension at least some of the way to the house.
Much obliged! Drew
Tags
capacitor , pump motor , wiring
Sump Pump Questions henlij Plumbing 22 03-16-2015 10:00 PM
Intermittent submersible pump fault esquilax Electrical 5 09-30-2011 03:56 AM
Sump pump operation MikeKy55 Plumbing 16 05-11-2011 04:35 PM
Well Pump Problems dannyjoe Plumbing 6 10-01-2009 06:10 PM
Modification to an existing pump switch DRBLKJK Electrical 10 08-23-2009 03:06 PM