Where should the ground for the cable and telephone systems go? I have heard they should have their own ground rod and and I have also heard that they should be connected to the electrical panel ground. What's the right way?
jerryh3 is offline   Reply With Quote
Old 06-16-2008, 06:40 PM   #2
Rewards Points: 266
They should be connected to the grounding electrode conductor and not their own ground rod.
junkcollector is offline   Reply With Quote
Old 06-16-2008, 07:29 PM   #3
Rewards Points: 6,652
If you want the NEC answer, then go to http://www.nfpa.org/freecodes/free_a....asp?id=7008SB As for your question, each would be connected to the nearest grounding point, and for both, would be a Cold Water pipe, that would have a Bonding jumper over the meter if in the house. Problem with that, is that some newer homes run Plastic water pipe to the home, then from there, it is usually PEX inside, or Copper. That means having to use a Ground rod outside.
Old 06-16-2008, 08:05 PM   #4
Electrician
You get 7 options.
Name:  800.40 (B)(1).jpg
Not required, but IF you do you need to bond the communications ground rod with the electrical ground rod with a jumper not smaller than #6 cu.
chris75 is offline   Reply With Quote
Old 06-16-2008, 08:21 PM   #5
Thanks. I only have Volume 1 of Holt's Understand the NEC. I'll probably hit the underground water service coming into the house. It's about 10 feet from the outdoor ground block of the coax(and telephone NID). Is option C just a jumper that runs to the grounding bar in the service panel?
Old 06-16-2008, 08:27 PM   #6
Electrician
Its a jumper run from the service disconnecting means, so its actually the point where you run the grounding electrode conductor to.
Old 06-16-2008, 08:29 PM   #7
Electrician
Dont forget, within 5' of where the water enters your house, and make sure its bonded to begin with...
Old 06-16-2008, 08:46 PM   #8
My grounding electrode conductor runs from the cold water pipe to the ground bus bar in the main service panel.
Old 06-16-2008, 08:55 PM   #9
Electrician
Good, I'm sure you have at least one ground rod as well... but your fine hitting the water to bond the CATV and Phone.
Old 06-16-2008, 08:59 PM   #10
No, I don't think I have a supplemental rod on the main panel. I only have a rod driven at my garage connected to the sub panel.
Old 06-16-2008, 09:06 PM   #11
Electrician
The garage detached?
Old 06-16-2008, 09:08 PM   #12
Yes. It's a four wire feed with the neutral and ground seperated.