Cable Sizes- A Bit Confused - Electrical - DIY Chatroom Home Improvement Forum
Old 05-28-2012, 04:30 PM   #1
Cable sizes- a bit confused
I need two sub panels and I want to run aluminum SER. I want to feed one with 60 amps and the other with 100 amps.
The supply house calls 2-2-2-4 AL SER "100 amp cable", however the code says differently the way I am interpreting it.
What size AL SER would I need to feed a 100A and 60A subpanel in a house?
FWIW, we are now on the 2011 code, but when I went to the supply house (and he told me 2-2-2-4 would work) we were on the 2008.
Thanks!
Macro is offline   Reply With Quote
Old 05-28-2012, 04:39 PM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Thanks!
First question, do you really need 100 amps? I personally would use #2 SER and just back it with a 90 amp breaker, #4 SER for the 60 amp panel...
Old 05-28-2012, 04:44 PM   #3
I'm wondering about what code allows. It seems to limit the #2 AL to 90A, but why would a huge supply house that services thousands of electrician commonly call that size "100A cable"? I ask because I have seen people discussing this before on other forums and from what I remember they had reasonable explanations why 100A was allowed on #2.
Old 05-28-2012, 04:46 PM   #4
Licensed electrician
Rewards Points: 1,766
The code changed and not everyone has kept up with the changes. What used to be able to be used as 100 amp cables is now 90 amp cable.
stickboy1375 (05-28-2012)
Old 05-28-2012, 04:53 PM   #5
What year was that change, do you remember?
Old 05-28-2012, 04:58 PM   #6
E2 Electrician
To be honest, its only good for 75 amps... if you are on the 2008 NEC... I was offering 90 amps off the 2005 NEC which I am on in Connecticut.
Old 05-28-2012, 04:59 PM   #7
Yup, but that was changed yet again in 2011. Now it's back to the old way as long as the romex or SER isn't in contact with insulation.
Old 05-28-2012, 05:02 PM   #8
E2 Electrician
The real problem started when people started using table 310.15(B)(6) for #2 SER as a feeder and not a service, it has always only been rated for 90 amps... so then the 2008 came out and enforced that you use the 60 degree column of 310.16 for type SE cables... that was the real killer.
Old 05-28-2012, 05:02 PM   #9
E2 Electrician
Thanks, i was unaware of that change again... I'm lucky to still be on 2005. So 90 amps it is... The real culprit is people misusing Table 310.15 (B)(6)...
Old 05-28-2012, 05:06 PM   #10
Now THAT makes sense, I just looked into it and it seems to be the reason for the confusion. It's a shame that a 90A breaker costs more than a 100A since it's a specialty item most places.
As for the 60A sub panel, if I use #4 SER, wouldn't I be able to step up to a 70A breaker?
Old 05-28-2012, 05:09 PM   #11
E2 Electrician
Sure, as long as the actual load isn't above 65 amps..
Its a shame supply houses and manufactures are not on board, because these devices should cost the same and be stocked.
Old 05-28-2012, 05:09 PM   #12
#4 Al SER would be limited to the 60 degree column of 55 amps.
Old 05-28-2012, 05:13 PM   #13
E2 Electrician
Im assuming it depends on what code cycle you are on? I can use the 75 degree column..
Bummer, you are correct. scratch the above.
Old 05-28-2012, 05:19 PM   #14
E2 Electrician
So where did the 90 amps EVER come into play then? Only the 2011 NEC, correct?
Old 05-28-2012, 05:24 PM   #15
If the #4 was copper and using the 75 degree column it would be 85 amps. The next standard size breaker is 90 amps so you can round up.
In-Floor Heating Cable Trouble... sootybuttercup Electrical 24 12-18-2014 08:01 PM
sound out of cable box amakarevic Home Theater 11 05-18-2012 10:26 AM
Is Tray Cable acceptable for Residential use? MisterSteve Electrical 43 02-21-2012 12:35 AM
broken drum snake cable, how to fix? confusedDIY Plumbing 1 03-18-2010 08:38 AM
Cable issue or wiring issue? Duchey Electrical 57 12-15-2008 01:34 PM