A/C Wiring Manual Says 14 Awg & 20 Amp Breaker? - Electrical - DIY Chatroom Home Improvement Forum
Old 06-16-2011, 11:45 AM   #1
Rewards Points: 16
A/C wiring manual says 14 awg & 20 amp breaker?
Wiring a mini-split a/c and the manual says use a 14 awg & 20A breaker.
I ran about twenty feet of 14 awg exterior sheathed solid wire through conduit at the panel through the exterior wall and to the outside condenser unit.
...*then* I read "use a 20A breaker"
I thought I was going to use a 15A breaker.
Can I use a 20A breaker with this wiring?
This is the manual. See page #24 of the .pdf
http://us.lge.com/download/product/f...%29_011607.pdf
Can this unit operate on a 15A breaker?
See page #11 (first column unit LAN091CNP / LAU091CNP)
brianosaur is offline   Reply With Quote
Old 06-16-2011, 11:48 AM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 140
Follow the instructions.
14 gauge wire and 20 amp breaker.
The Following 2 Users Say Thank You to jbfan For This Useful Post:
electures (06-16-2011), J. V. (06-16-2011)
Old 06-16-2011, 11:50 AM   #3
Rewards Points: 16
...yeah but isn't code 12/20?
Old 06-16-2011, 11:56 AM   #4
jbfan's Avatar
Rewards Points: 140
Code is follow the instructions of the manufacturer.
A/C circuits have their own rules about size and ocp
Jim Port (06-17-2011), SD515 (06-16-2011)
Old 06-16-2011, 12:05 PM   #5
Rewards Points: 16
ok sounds good
Old 06-16-2011, 06:07 PM   #6
Electrician
Rewards Points: 760
Code will also tell you to use #14 on a 20A breaker.
Your unit does not use more then 15A when it is running, but when it starts it needs the extra bit to get itself going, that is why it goes on a 20A breaker.
darren is offline   Reply With Quote
Old 06-16-2011, 06:19 PM   #7
Wire Chewer
Red Squirrel's Avatar
Rewards Points: 46
Personally I would try a 15 amp breaker and if it trips then go with the 20. Seems kinda odd they would go against standard conventions though.
Old 06-16-2011, 06:51 PM   #8
Electrician
SD515's Avatar
Rewards Points: 504
As jb mentioned, AC’s have some different rules, and one of them is that a larger breaker can be used than you would typically for a given gauge of wire. I see your line of thinking Red Sq, but if anything should be changed, I would change to 12ga wire. You can always use a larger wire. Not that the OP has too though, as per the instructions.
Kyle
Old 06-16-2011, 08:53 PM   #9
kbsparky's Avatar
The section of the Code [240.4(D)] that requires 15 Amp max on circuits fed with 14 AWG does not apply in cases of HVAC circuits.
A different section [240.4(G)] applies, where such limitations are removed.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
electures (06-17-2011)
Old 06-16-2011, 10:33 PM   #10
Wire Chewer
Rewards Points: 46
Originally Posted by SD515 View Post
As jb mentioned, ACís have some different rules, and one of them is that a larger breaker can be used than you would typically for a given gauge of wire. I see your line of thinking Red Sq, but if anything should be changed, I would change to 12ga wire. You can always use a larger wire. Not that the OP has too though, as per the instructions.
Yeah was thinking that too, but figured maybe they said 14 awg because of how the wire connects at the other end or something. But if it's just a screw terminal no reason not to just use 12awg. Or terminate at a junction box then switch to 14awg.
The way I see it, if by chance something else was added to that circuit, you don't want to overload the wire. Now this should not happen in first place, but always good to be safe.
Old 06-17-2011, 07:01 AM   #11
Lic Elect/Inspector/CPO
Most Minisplits use 14 wire. It listed as a communication cable, which is listed for outside use and is sunlight resistant. Use what the mfg says to use. Some minisplit such as Fujitsu, will not work properly with splices. That info came from Fujitsu tech support.
I just had a cervice call on one of these. There was a splice. Ran new 14 communication wire and the unit worked fine.
The inside unit gets it powewr from the outside unit. There is a signal wire, which tells the outside unit when to turn on or off. This signal is dc and needs a direct connection to each unit.
NJMarine is offline   Reply With Quote
Old 06-17-2011, 10:08 AM   #12
Rewards Points: 16
It wasnt in the a/c install manual but,
I also read somewhere that a visible shutoff switch is needed near the outside unit.
Should I put one in along the cable mentioned?
Old 06-17-2011, 01:45 PM   #13
Wire Chewer
Rewards Points: 46
I would do it just for convinience sake. Good to close it in winter so you don't accidentally turn it on from inside when it is covered.
Old 06-17-2011, 04:57 PM   #14
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
I disconnect is required within site of the unit. Does not have to be fused unless nameplate requires it. A knife switch will comply.
electures is offline   Reply With Quote
Distance between the main breaker panel and a manual transfer switch panel jerryallie Electrical 2 09-01-2010 09:11 PM
Breaker box wiring question(s) janralix Electrical 6 08-29-2010 11:13 PM
Wiring help BenJoeM Electrical 15 10-28-2008 08:59 AM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 09:59 PM