A/C Condenser Disconnect Box - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 03-19-2013, 04:13 PM   #16
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by al_smelter View Post
Have you had trouble with the fusing in the past? If not, don't re-invent your own wheel. Simply leave the 30 amp fuses in place.
Remember, you don't even need fuses if the breaker at the panel is correct for the wire size (which we earlier established is the case). So if you decide you just want to change the disconnect, buy a non-fused model (30 amp) and be done with it.
He could use #12 AWG and still use 35 amp fuses...
Old 03-20-2013, 06:55 AM   #17
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Not Romex.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
jbfan (03-20-2013)
Old 03-20-2013, 05:51 PM   #18
E2 Electrician
Originally Posted by electures View Post
Not Romex.
Still on 2005, I have a hard time accepting that when I leave Connecticut, it's all of a sudden an issue.
Old 03-22-2013, 09:45 AM   #19
electures's Avatar
Now that is funny right there!! Git-r-dun!!
stickboy1375 (03-22-2013)
Central Air Condenser Disconnect Skelleyman HVAC 54 04-27-2012 03:44 AM
Central Air Condenser Disconnect Skelleyman Electrical 15 04-21-2012 11:15 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
Goodman Fan Condenser Replacement Help bigjohnstud4200 HVAC 2 07-03-2010 01:54 PM
Moving condenser electrical disconnect, required? Dave Carney HVAC 7 07-27-2009 10:34 PM