A/C Condenser Circuit Size - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-29-2011, 03:52 PM   #16
Electrical Contractor
Originally Posted by Speedy Petey View Post
No, it's an air conditioner.
That's what I'm saying, you can't put a #12 on something that pulls 30amps. 25A max, even then I would use #10.
Sine is offline   Reply With Quote
Old 10-29-2011, 04:50 PM   #17
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,948
Oh, sorry. I misunderstood.
Old 10-29-2011, 04:51 PM   #18
You're right, my bad. I Typically just use the name plate and don't have to refer back to Article 440.
Yup, SOP.
Everything we need is right on that label.
Old 10-29-2011, 04:57 PM   #19
Lic Elect/Inspector/CPO
Breaker to wire size is not always black and white. Such as #10 on a 30 amp breaker.
Breaker sizes for motors, welders and A/C units follow different rules than other branch circuits. So to say #12 on a 30 amp breaker is wrong, is, well, wrong
NJMarine is offline   Reply With Quote
Old 10-30-2011, 10:19 AM   #20
That is not what we were saying. If you read back you will see that the MCA or minimum circuit ampacity was 30A.
Old 10-30-2011, 06:20 PM   #21
using 12 for a min 30 ampac unit is allowed. As I stated before it is done all the time. While some may say pull 10 wire that is fine. I was just saying what is allowed by the code.
Old 10-30-2011, 06:28 PM   #22
Code05's Avatar
Rewards Points: 1,104
If the MCA is 30, you cannot use #12. You can put #12 on a larger breaker for motors and such, but the MCA has to be 25 or less amps.
Code05 is offline   Reply With Quote
Old 10-30-2011, 06:51 PM   #23
Code05's Avatar
The smallest 100% rated breaker that I know of is 400 amps and goes into a 1200 amp switchgear.
Old 10-30-2011, 07:15 PM   #24
Just because it is done all the time doesn't make it permissible by code.
Need a wiring diagram Mooreski Electrical 47 02-01-2015 03:07 PM
Rewiring furnace electrical circuit BlueBSH HVAC 4 09-21-2010 01:34 PM
Open circuit has power, close the circuit no power??? BeginnerHomeDIY Electrical 7 07-08-2009 02:40 PM
Circuit advice for finishing basement Straightgrain Electrical 16 03-25-2009 09:07 AM
Circuit breakers and wire size stan 41943 Electrical 19 03-06-2008 02:29 PM