Burying Ground Rod - Electrical - DIY Chatroom Home Improvement Forum
Old 11-06-2008, 09:50 PM   #1
burying ground rod
I believe I read here that rather than driving a ground rod you can bury one 24" deep (I plan to drive the 2nd for my subpanel the ole fashioned way). Since I will be trenching to run the electrical to my garage, is it acceptable to bury the ground rod in that same trench (it will be aligned in the same fashion as the electrical run)?
joey b is offline   Reply With Quote
Old 11-07-2008, 09:16 AM   #2
joed's Avatar
Rewards Points: 12,448
Burying in that fashion is only permitted IF you have rock or something that prevents driving straight in.
I found the code section
"250.53(g) shall be driven to a depth of not less than 8' ,except that where rock bottom is encountered it ....."
The rest says up to 45 angle unles you can't get that either then a trench 30" deep can be used.
Old 11-07-2008, 09:22 AM   #3
Electrician
Rods should always be driven first, then at a 45 degree 2nd, and if all else fails, it is allowed to lay a rod in at least 2' 6" of soil, but you still need two rods and the garage and they need to be 6' apart.
All rod and pipe electrodes must have at least 8 ft of length in contact with the soil,
regardless of rock bottom. Where rock bottom is encountered, the electrodes must
either be driven at not more than a 45-degree angle or buried in a 2 1/ 2-ft-deep trench.
It should be noted that driving the rod at an angle is permitted only if it is not possible
to drive the rod vertically to obtain at least 8 ft of earth contact. Burying the ground rod
is permitted only if it is not possible to drive the rod vertically or at an angle.
Ground clamps used on buried electrodes must be listed for direct earth burial. Ground
clamps installed aboveground must be protected where subject to physical damage.
chris75 is offline   Reply With Quote
Old 11-07-2008, 09:33 AM   #4
joed's Avatar
You could use a plate electrode. They only need to be buried minimum 30" deep.
250.53(h)
To ground or not to ground, that is the question cartalker Electrical 8 10-18-2008 10:12 AM
Temporary Genrator Ground theatretch85 Electrical 32 08-05-2008 12:05 PM
Ground question. mystery guest Electrical 5 07-24-2008 12:47 PM
Older home -- Open Ground issues, please help Toyz Electrical 1 06-15-2008 08:41 AM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 06:30 PM