There is probably nothing wrong except that the set screws where the wires are burned were not tightened down.
Even if you had 20 ampere fuses on the 14 gauge wires (improper), the dishwasher and disposer under normal use aren't going to be drawing enough power long enough to burn the wires with no loose connection.
A loose connection can lead to overheating of that kind with less than a quarter of the amperes rating being drawn, thus the breaker does not trip. It is possible that just one loose connection got the metal terminal strip (bus bar) so hot that wires in neighboring slots got burned also.
The Following 2 Users Say Thank You to AllanJ For This Useful Post:
Kyle_in_rure (03-31-2013), mpoulton (04-01-2013)
Old 04-01-2013, 11:46 AM   #17
Thanks for the explanation. This makes sense. Also the breaker is 15 amps.
greencat is offline   Reply With Quote
Old 04-01-2013, 12:26 PM   #18
Always learning...
fetzer85's Avatar
Rewards Points: 262
While we're on this topic, does code give any specific torque specs for the buss bar screws? All mine are 'tight' but anytime I see a problem like this happen I figure the more details we can share the better. Thanks
fetzer85 is offline   Reply With Quote
Old 04-01-2013, 02:00 PM   #19
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
No. Follow the manufacturers installation instructions.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
fetzer85 (04-01-2013)
Can you use wire nuts on a fan light switch with silvery looking wires? amodoko Electrical 4 10-28-2012 08:26 PM
Are Dead wires allowed or unsafe? Scooby333 Electrical 31 10-01-2012 01:26 PM
240v conduit with different gauge wires... Biospot Electrical 7 12-14-2010 07:07 PM
Removing wall with wires in it jboswald Electrical 11 11-29-2009 02:55 PM
Three hot wires coming into a receptacle? Jeff DIY Electrical 10 10-07-2009 01:35 PM