Burnt Wires - Electrical - DIY Chatroom Home Improvement Forum
Old 03-31-2013, 06:32 PM   #1
Burnt Wires
Hi
My dishwasher and garbage disposal stopped working. I knew they were on the same circuit. I checked the power with volt meter and could only see power if I touched the black and ground wires. White did not work.
Took off the breaker panel and saw the burnt wires. See attached. This home is 3 years old and thought the wiring was OK.
Why didn't the breaker flip?
I installed the disposal 3 years ago and used the same circuit as the dishwasher. Do you think that caused the problem - running the dishwasher and disposal at the same time? The dishwasher was replaced 2 years ago and the new one has a sanitized wash mode that heats the water - could that be the problem.
What do you think caused the problem? Thanks
greencat is offline   Reply With Quote
Old 03-31-2013, 06:35 PM   #2
for starters, if you knew the dishwasher and the garbage disposal were on the same circuit, you should have done something to rectify that.
They dont belong on the same circuit according to the NEC.
And if the circuit didnt trip, you could have oversized the conductors, or faulty breaker.
Ya live and you learn, count your blessings here
jratftcc is offline   Reply With Quote
Old 03-31-2013, 06:44 PM   #3
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
Originally Posted by greencat View Post
Hi
1) are the lugs TIGHT ???
2) are there any RED wires in the panel ??? the burnt ones are white ... ( well used to be )
if so how many ??
Philly Master is offline   Reply With Quote
Old 03-31-2013, 07:07 PM   #4
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Really. Code section?
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following 3 Users Say Thank You to electures For This Useful Post:
k_buz (03-31-2013), micromind (03-31-2013), sirsparksalot (04-01-2013)
Old 03-31-2013, 07:16 PM   #5
dmxtothemax's Avatar
Rewards Points: 5,108
Hi
Looks like the damage was caused by heat build up !
WHY ?
either the wires were overloaded,
or there was a poor connecttion between
the wires and the terminal block.
Remember at high power, just a little extra
resistance can generate a lot of heat.
so it's vitally important to use correct sized wires
and make sure the connecttions are clean and good !
Possibbly one or more wires have worked loose.
Wires will expand slightly each time they are used,
so - expand - contract - expand - contract, etc
can lead to loose connections
dmxtothemax is offline   Reply With Quote
Old 03-31-2013, 07:18 PM   #6
electures's Avatar
WHat size is the GD?
Old 03-31-2013, 07:37 PM   #7
" Euro " electrician
frenchelectrican's Avatar
First of all .,
1) how many amps do that dishwasher is running ? ( look at the nameplate for that info )
2) How many amps garbage dispoal unit is running ? ( again look for nameplate )
3) Not sure if this is correct on the photo look like ya got 2.5mm2 ( 14 gauge ) and what breaker size this is on ?
4) look like one of the screws on netural bussbar is not really tightend down properly.
Do you have any mulitwire branch circuits ? If so are they in correct postion ?
I have a feeling the dishwasher is pretty close to the limit of that circuit but I will wait for your reply on nameplate info before I can go further.
Merci,
Marc
Old 03-31-2013, 07:53 PM   #8
Civil Engineer
Rewards Points: 4,574
I think Frenchelectrician nailed it, those white wires (presumably the neutrals) look like they are all 14 gage. Possibly you have 20A breakers with 14 gauge wire? If so it is entirely possible to overload the wire with 20A or even a little more and not trip the breaker. Given the number of burned wires, this may be a systemic problem in your house.
Daniel Holzman is online now   Reply With Quote
The Following User Says Thank You to Daniel Holzman For This Useful Post:
frenchelectrican (03-31-2013)
Old 03-31-2013, 08:00 PM   #9
Bonjour Dan.,
I think the OP's situatuion may be worst than that and I will ask the OP to take a photo of whole panel to see what is going on and I have a feeling something is not adding up right with this.
To OP will you take a photo of whole panel this way we can get the facts in better this way and the photo will tell us the story what is going on.
I think there is something more going on with this.
Merci,
Marc
Old 03-31-2013, 09:11 PM   #10
Rewards Points: 30
first, i am not an electrician.
I agree with all of the above posts.
to see at least 6 neutrals in a row burned as badly as these are something is terribly wrong. the ones in the middle of the neutral bar are the ones suspect.
I would inspect the entire box. Are any others showing discoloring? trace out where all burnt wires are going. check all devises wired to any of thoswe circuits. It may be a space heater or other high draaw device on any of those wires, not just the dishwasher/ gd.
pictures
bernie
bernie963 is offline   Reply With Quote
Old 03-31-2013, 09:11 PM   #11
Thanks for your responses. The breaker is 15 amps and there are no red wires. Locks like only 1 wire burned but 4 above that wire melted. Attached are more pictures. The specifications for the dishwasher is 15 amps don't know if it draws that much.
Old 03-31-2013, 09:15 PM   #12
Replying to another comment. We don't have any high draw items.
Old 03-31-2013, 09:44 PM   #13
The label on the dishwasher says 9.4 amps. I think the burning took place a while ago since I don't smell any burning but remember a burning smell about a month ago. I had added the gb to the dishwasher circuit since they normally don't run at the same time.
I wonder if it was a lose lug since the breaker didn't trip and the dishwasher worked for a month after burning.
Old 03-31-2013, 09:48 PM   #14
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Looks like a classic loose connection to me.
The Following 3 Users Say Thank You to k_buz For This Useful Post:
Kyle_in_rure (03-31-2013), mpoulton (04-01-2013), stickboy1375 (03-31-2013)
Old 03-31-2013, 10:26 PM   #15
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
14 AWG is actually rated for 20 amps, the NEC is what forbids us in using it in this manner, so we can rule out that assumption right now.
The Following User Says Thank You to stickboy1375 For This Useful Post:
Can you use wire nuts on a fan light switch with silvery looking wires? amodoko Electrical 4 10-28-2012 09:26 PM
Are Dead wires allowed or unsafe? Scooby333 Electrical 31 10-01-2012 02:26 PM
240v conduit with different gauge wires... Biospot Electrical 7 12-14-2010 08:07 PM
Removing wall with wires in it jboswald Electrical 11 11-29-2009 03:55 PM
Three hot wires coming into a receptacle? Jeff DIY Electrical 10 10-07-2009 02:35 PM